USB Badge Reader
Hello All,
I have a USB badge reader, that I'd like to use for authenticating users to access a touch panel. I have a CSV file of all of the users that are allowed access. I'm trying to figure out the best way to program the panel for authentication. Basically, the badge reader just works as a keyboard function, inputting the badge ID number when it's scanned.
Matt
  • PhreaKPhreaK Posts: 966
    If this is a standard HID device you may be able to attach it to an X or S Series panel and have it function the same way as an external keyboard. On you're UI you will then need a 'text input' button (you can set this under the 'General' tab in the button properties editor). You can also have this hidden (opacity: 0) so that this input side stays completely transparent to your users.
    When text comes in from this it will then fill into this button. From here you a couple of options:
    1) Add a button with it's port set to the loopback port (0) and channel of 'Keyboard: Exit'. When pressed this will fire the contents of all of your text inputs on that page back to the master as a string event prefixed with the text input button's name. Depending on your desired interaction pattern you could also have this hidden and use a do_push *shudder* at say a one second interval when your are in this area of your UI.
    2) Alternatively, you could query the contents of this button at a set interval. This would keep all controls hidden and enable your users to auth etc just by the physical interaction with the reader.
  • PhreaK wrote: »
    Hey Kim,
    Thanks so much for the help! I am trying to do exactly what you thought, hooking it directly to the panel and using it as the keyboard function. What I think I am going to need the most help with is getting it to authenticate based on the numbers it reads. I have a CSV file with all of the badge numbers available, but how do I get the master to check against these numbers?
    If you could provide any netlinx code I'd appreciate any help I can get!
    THANKS!
    With that you will probably just want to read the CSV into a structure at boot or if it is being updated regularly if you cannot identify a user following the first attempt. I actually did something very similar to this to provide the functionality we would normally get from LDAP at a trade show down here in Australia a few weeks back. You can see the bit of code that does the CSV read here. The explode function that it uses is from the NetLinx Common Libraries.
    Depending on your environment though (number of users, frequency of updates etc.) you may want to store this sort of data in an external service though and query it as required.
  • PhreaK wrote: »
    Thanks Kim,
    I'm a novice programmer, so I think this is going to be way above my head. For testing of the equipment purposes, is there a simple way to see if the reader is working and make it flip pages?
    Matt
    Sure is. If you just want to see if the reader works before diving in too deep just create a touch panel file with a single page and pop a text input button on there. Plug your reader in and see if it fills with content when a read takes place. If so, you're reader is compatible.
    Also, don't be afraid I've diving into something that seems over your head. If you keep doing what your comfortable doing you never have any fun :)
  • PhreaK wrote: »
    Okay thanks,
    So I tried that, and sure enough it did read the badge and numbers appeared in the box. Without getting overly complicated for now, how would I create a string of code in netlinx that would authenticate a page flip based on if only my badge ID was entered? I'll dive into the CSV file and all that once I get a better sense of what I'm doing! Thanks for the words of encouragement! You seem like a very talented programmer.
    Matt
    Awesome. If you have a look at the programmers guide for your touch panel you will be able to find a few commands in there for reading button text as well as setting it. A nice approach to implementing this may be to have a timeline (check the NetLinx Keywords help from NetLinx Studio for some info on these if you haven't played with them in the past) that checks to see if there's something in here the same length as your card ID's say once a second. If there is you then you have an ID to auth and can clear this out (again, check the programmers guide for the syntax to set button text) so that it's ready for your next read. As I mentioned before you can then make this text input button completely transparent if you like so that a user can walk up to panel and just auth with their card without even noticing what goes on behind the scenes.
  • PhreaK wrote: »
    Been fooling around with this all day: Can't seem to get it to work just for basic testing. Any ideas where I'm going wrong?
    PROGRAM_NAME='Keypad Testing'
    dvTP = 10001:1:0 //AMX Modero NXTCV10
    dvMaster = 0:1:0 //NI700 Master Controller
    SEND_COMMAND dvTP, "'?TXT-1,0'"
    NON_VOLATILE char Text[11]
    DATA_EVENT[dvTP]
    ONLINE:
    SEND_COMMAND dvTP, 'PAGE-Swipe'
    BUTTON_EVENT[dvTP,212]
    IF(Text == '13960017776')
    SEND_COMMAND dvTP, 'PAGE-Error'
    ELSE
    SEND_COMMAND dvTP, 'PAGE-Main'
  • IT WORKED!
    I was able to use one badge id to authenticate... now how to get multiple badges using a text file is the next step..
    NON_VOLATILE CHAR Text
    SEND_COMMAND dvTP, "'^TXT-1,3',ITOA(Text)"
    DATA_EVENT[dvTP]
    ONLINE:
    SEND_COMMAND dvTP, 'Page-Swipe'
    STRING:
    IF
    (FIND_STRING(DATA.TEXT,'139600177',1))
    SEND_COMMAND dvTP, 'Page-Main'
    ELSE
    SEND_COMMAND dvTP, '@PKP'
  • Attached is some code I used to test the NFC functionality. You should be able to adapt this for your USB reader. This code taps into custom event 700 which occurs when the panel reads an NFC card. It uses a file named NFCPriv.txt to hold the data which includes the starting page to flip to when the user logs in. FTP the data file to the master for use. Instead of triggering on the custom event, adapt this to use your string event.
    Please note that this code has been edited from a MUCH larger file that tests lots of different things. I know it compiles and I think it will work OK but I don't have any hardware to test it with at the moment so YMMV.
  • GregGGregG Posts: 251
    And where can the normal rabble like us find the list of secret magic event codes? ;-)
  • This particular one is not secret. For example, see page 127 of the Modero X Programming Guide. As for the others...
  • PhreaK wrote: »
    Kim:
    My read_file function continually truncates the length of cSUBJECT with objects that I cannot see in Debug. For whatever reason, it thinks there is a comma or space in the CSV file. Can you tell what I'm doing wrong?
    DEFINE_FUNCTION fnREAD_FILE_MTG (CHAR cFILENAME[])
        LOCAL_VAR SLONG slFILE_VAL
        slFILE_VAL = FILE_OPEN(cFILENAME,FILE_READ_ONLY)
        IF(slFILE_VAL < 0)
    	SELECT
    	    ACTIVE(slFILE_VAL == -2): SEND_STRING 0, "'Invalid Path'"
    	    ACTIVE(slFILE_VAL == -3): SEND_STRING 0, "'Invalid Value'"
    	    ACTIVE(slFILE_VAL == -5): SEND_STRING 0, "'I/O Error'"
    	    ACTIVE(slFILE_VAL == -14):SEND_STRING 0, "'Max Files Open'"
    	    ACTIVE(slFILE_VAL == -15):SEND_STRING 0, "'Invalid File Format'"
        ELSE IF(slFILE_VAL > 0)
    	LOCAL_VAR SLONG slVAL
    	LOCAL_VAR INTEGER i
    	LOCAL_VAR CHAR cBUFF[120]
    	FOR(i=1; i<=MAX_LENGTH_ARRAY(uMTG); i++)
    	    slVAL = FILE_READ_LINE(slFILE_VAL,cBUFF,MAX_LENGTH_ARRAY(cBUFF))
    	    uMTG[i].cHOST_NAME = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cHOST_NAME,LENGTH_ARRAY(uMTG[i].cHOST_NAME)-1)
    	    uMTG[i].cSTART_DATE = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cSTART_DATE,LENGTH_ARRAY(uMTG[i].cSTART_DATE)-1)
    	    uMTG[i].cSTART_HOUR = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cSTART_HOUR,LENGTH_ARRAY(uMTG[i].cSTART_HOUR)-1)
    	    uMTG[i].cSTART_MINUTE = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cSTART_MINUTE,LENGTH_ARRAY(uMTG[i].cSTART_MINUTE)-1)
    	    uMTG[i].cEND_HOUR = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cEND_HOUR,LENGTH_ARRAY(uMTG[i].cEND_HOUR)-1)
    	    uMTG[i].cEND_MINUTE = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uMTG[i].cEND_MINUTE,LENGTH_ARRAY(uMTG[i].cEND_MINUTE)-1)
    	    uMTG[i].cSUBJECT = REMOVE_STRING(cBUFF, ',',1)
    	    IF(i > MAX_LENGTH_ARRAY(uMTG))
    		BREAK;
    	FILE_CLOSE(slFILE_VAL)
    Have you got you uMTG definition handy for reference?
    One thing I see as a possibility from the code below is your cBUFF variable is only 120 characters. This will result in a max line length of 120. As your subject is the last column of that CSV format it will be the item that is truncated during the read line.
  • PhreaK wrote: »
    I've attached code for reference. I tried to solve the cBUFF issue by having it ignore commas or blank space, but I'd prefer not to. Any tips would be helpful. I changed the cBUFF length back to 2048, what should it be?
    PROGRAM_NAME='Calendar Demo Rev 1'
    (*  FILE CREATED ON: 01/16/2015  AT: 08:00:17              *)
    (*  FILE_LAST_MODIFIED_ON: 02/03/2015  AT: 07:17:07        *)
    dvMaster	=	0:1:0
    dvTP		=	10001:1:0
    dvTP_Locked	=	10001:3:0
    dvTP_Mtg	=	10001:4:0
    (*               CONSTANT DEFINITIONS GO BELOW             *)
    DEFINE_CONSTANT
    MAX_USERS = 500
    MAX_MEETINGS = 36
    TL_FEEDBACK = 1
    TL_FEEDBACK2 = 2
    TL_FEEDBACK3 = 3
    (*              DATA TYPE DEFINITIONS GO BELOW             *)
    DEFINE_TYPE
    STRUCTURE _sUSERS //Presets Structure
        CHAR cID[15]
        CHAR cFIRST_NAME[25]
        CHAR cLAST_NAME[25]
        CHAR cEMAIL[50]
    STRUCTURE _sMTG //Mtg Structure
        CHAR cHOST_NAME[25]
        CHAR cSTART_DATE[25]
        CHAR cSTART_HOUR[4]
        CHAR cSTART_MINUTE[4]
        CHAR cEND_HOUR[4]
        CHAR cEND_MINUTE[4]
        CHAR cSUBJECT[50]
    PERSISTENT _sUSERS uUSERS[MAX_USERS]
    PERSISTENT _sMTG uMTG[MAX_MEETINGS]
    VOLATILE CHAR cDATA[25]
    VOLATILE CHAR cBADGE[20]
    VOLATILE INTEGER nVALID_ENTRY
    VOLATILE INTEGER nDONE
    VOLATILE CHAR cHOST_NAME[25]
    VOLATILE CHAR cSTART_DATE[25]
    VOLATILE CHAR cSTART_HOUR[4]
    VOLATILE CHAR cSTART_MINUTE[4]
    VOLATILE CHAR cEND_HOUR[4]
    VOLATILE CHAR cEND_MINUTE[4]
    VOLATILE CHAR cSUBJECT[50]
    VOLATILE INTEGER nMINUTE
    VOLATILE INTEGER nHOUR
    VOLATILE INTEGER nMINUTE2
    VOLATILE INTEGER nHOUR2
    VOLATILE INTEGER nTIME
    NON_VOLATILE sINTEGER nCURRENT_HOUR
    NON_VOLATILE sINTEGER nCURRENT_MIN
    NON_VOLATILE sINTEGER nCURRENT_MEETING
    VOLATILE LONG nTIMER[] = {500}
    VOLATILE LONG nTIMER2[] = {5000}
    VOLATILE LONG nTIMER3[] = {10000}
    VOLATILE INTEGER nCLOSED
    NON_VOLATILE DEVCHAN dcMTGs[] =
    {dvTP_Locked, 1},
    {dvTP_Locked, 2},
    {dvTP_Locked, 3},
    {dvTP_Locked, 4},
    {dvTP_Locked, 5},
    {dvTP_Locked, 6},
    {dvTP_Locked, 7},
    {dvTP_Locked, 8},
    {dvTP_Locked, 9},
    {dvTP_Locked, 10},
    {dvTP_Locked, 11},
    {dvTP_Locked, 12},
    {dvTP_Locked, 13},
    {dvTP_Locked, 14},
    {dvTP_Locked, 15},
    {dvTP_Locked, 16},
    {dvTP_Locked, 17},
    {dvTP_Locked, 18},
    {dvTP_Locked, 19},
    {dvTP_Locked, 20},
    {dvTP_Locked, 21},
    {dvTP_Locked, 22},
    {dvTP_Locked, 23},
    {dvTP_Locked, 24},
    {dvTP_Locked, 25},
    {dvTP_Locked, 26},
    {dvTP_Locked, 27},
    {dvTP_Locked, 28},
    {dvTP_Locked, 29},
    {dvTP_Locked, 30},
    {dvTP_Locked, 31},
    {dvTP_Locked, 32},
    {dvTP_Locked, 33},
    {dvTP_Locked, 34},
    {dvTP_Locked, 35},
    {dvTP_Locked, 36}
    (*               LATCHING DEFINITIONS GO BELOW             *)
    DEFINE_LATCHING
    (*       MUTUALLY EXCLUSIVE DEFINITIONS GO BELOW           *)
    DEFINE_MUTUALLY_EXCLUSIVE
    (*        SUBROUTINE/FUNCTION DEFINITIONS GO BELOW         *)
    DEFINE_FUNCTION INTEGER fnCONVERT_REQUEST (INTEGER nSTART_HOUR, INTEGER nSTART_MINUTE, INTEGER nEND_HOUR, INTEGER nEND_MINUTE)
        STACK_VAR INTEGER nDURATION
        STACK_VAR i
        STACK_VAR x
        IF(nSTART_HOUR == 1)
    	nSTART_HOUR = 13
        ELSE IF(nSTART_HOUR == 2)
    	nSTART_HOUR = 14
        ELSE IF(nSTART_HOUR == 3)
    	nSTART_HOUR = 15
        ELSE IF(nSTART_HOUR == 4)
    	nSTART_HOUR = 16
        IF(nEND_HOUR == 1)
    	nEND_HOUR = 13
        ELSE IF(nEND_HOUR == 2)
    	nEND_HOUR = 14
        ELSE IF(nEND_HOUR == 3)
    	nEND_HOUR = 15
        ELSE IF(nEND_HOUR == 4)
    	nEND_HOUR = 16
        ELSE IF(nEND_HOUR == 5)
    	nEND_HOUR = 17
        i = ((nEND_HOUR - nSTART_HOUR)*60)
        x = nEND_MINUTE - nSTART_MINUTE
        nDURATION = i + x
        RETURN nDURATION
    DEFINE_FUNCTION INTEGER fnPROCESS_TIME (INTEGER nHOUR, INTEGER nMINUTE)
        STACK_VAR INTEGER t
        IF(nHOUR > 12)
    	nHOUR = nHOUR - 12
        IF(nHOUR == 8 && nMINUTE < 15)
    	t = 1
        ELSE IF(nHOUR == 8 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 2
        ELSE IF(nHOUR == 8 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 3
        ELSE IF(nHOUR == 8 && nMINUTE >= 45)
    	t = 4
        ELSE IF(nHOUR == 9 && nMINUTE < 15)
    	t = 5
        ELSE IF(nHOUR == 9 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 6
        ELSE IF(nHOUR == 9 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 7
        ELSE IF(nHOUR == 9 && nMINUTE >= 45)
    	t = 8
        ELSE IF(nHOUR == 10 && nMINUTE < 15)
    	t = 9
        ELSE IF(nHOUR == 10 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 10
        ELSE IF(nHOUR == 10 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 11
        ELSE IF(nHOUR == 10 && nMINUTE >= 45)
    	t = 12
        ELSE IF(nHOUR == 11 && nMINUTE < 15)
    	t = 13
        ELSE IF(nHOUR == 11 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 14
        ELSE IF(nHOUR == 11 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 15
        ELSE IF(nHOUR == 11 && nMINUTE >= 45)
    	t = 16
        ELSE IF(nHOUR == 12 && nMINUTE < 15)
    	t = 17
        ELSE IF(nHOUR == 12 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 18
        ELSE IF(nHOUR == 12 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 19
        ELSE IF(nHOUR == 12 && nMINUTE >= 45)
    	t = 20
        ELSE IF(nHOUR == 1 && nMINUTE < 15)
    	t = 21
        ELSE IF(nHOUR == 1 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 22
        ELSE IF(nHOUR == 1 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 23
        ELSE IF(nHOUR == 1 && nMINUTE >= 45)
    	t = 24
        ELSE IF(nHOUR == 2 && nMINUTE < 15)
    	t = 25
        ELSE IF(nHOUR == 2 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 26
        ELSE IF(nHOUR == 2 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 27
        ELSE IF(nHOUR == 2 && nMINUTE >= 45)
    	t = 28
        ELSE IF(nHOUR == 3 && nMINUTE < 15)
    	t = 29
        ELSE IF(nHOUR == 3 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 30
        ELSE IF(nHOUR == 3 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 31
        ELSE IF(nHOUR == 3 && nMINUTE >= 45)
    	t = 32
        ELSE IF(nHOUR == 4 && nMINUTE < 15)
    	t = 33
        ELSE IF(nHOUR == 4 && nMINUTE >= 15 && nMINUTE < 30)
    	t = 34
        ELSE IF(nHOUR == 4 && nMINUTE >= 30 && nMINUTE < 45)
    	t = 35
        ELSE IF(nHOUR == 4 && nMINUTE >= 45)
    	t = 36
        RETURN t
    DEFINE_FUNCTION INTEGER fnFILL_CALENDAR (INTEGER nHOUR, INTEGER nMIN)
        STACK_VAR INTEGER x
        STACK_VAR INTEGER nINDEX
        FOR(x=1; x<=MAX_LENGTH_ARRAY(uMTG); x++)
    	IF(LENGTH_ARRAY(uMTG[x].cSUBJECT) > 0)
    	    IF(uMTG[x].cSUBJECT == uMTG[x].cSUBJECT)
    		ON[dvTP_Locked, x]
    	ELSE
    	    OFF[dvTP_Locked, x]
        IF(nHOUR > 12)
    	nHOUR = nHOUR - 12
        nINDEX = fnPROCESS_TIME(nHOUR, nMIN)
        IF(LENGTH_ARRAY(uMTG[nINDEX].cSUBJECT) > 0)
    	SEND_COMMAND dvTP, "'^TXT-1,0,',uMTG[nINDEX].cSUBJECT"
    	RETURN TRUE
        ELSE
    	SEND_COMMAND dvTP, "'^TXT-1,0,Vacant'"
    	RETURN FALSE
    DEFINE_FUNCTION INTEGER fnPROCESS_REQUEST (INTEGER nINDEX, INTEGER nNUM_MTGs)
        STACK_VAR INTEGER i
        IF(LENGTH_ARRAY(uMTG[nINDEX].cSUBJECT) < 1)
    	FOR(i=1; i<=nNUM_MTGs; i++)
    		RETURN TRUE
    	    ELSE IF(LENGTH_ARRAY(uMTG[nINDEX].cSUBJECT) > 1)
    		RETURN FALSE
    		BREAK;
    	    nINDEX++
    DEFINE_FUNCTION fnRead_BadgeID (CHAR cFILENAME[])
        IF(slFILE_VAL < 0)
    	SELECT
    	LOCAL_VAR INTEGER i
    	LOCAL_VAR CHAR cBUFF[2048]
    	FOR(i=1; i<=MAX_LENGTH_ARRAY(uUSERS); i++)
    	    uUSERS[i].cID = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uUSERS[i].cID,LENGTH_ARRAY(uUSERS[i].cID)-1)
    	    uUSERS[i].cFIRST_NAME = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uUSERS[i].cFIRST_NAME,LENGTH_ARRAY(uUSERS[i].cFIRST_NAME)-1)
    	    uUSERS[i].cLAST_NAME = REMOVE_STRING(cBUFF,',',1)
    	    SET_LENGTH_ARRAY(uUSERS[i].cLAST_NAME,LENGTH_ARRAY(uUSERS[i].cLAST_NAME)-1)
    	    uUSERS[i].cEMAIL = cBUFF
        IF(slFILE_VAL < 0)
    	SELECT
    	LOCAL_VAR INTEGER i
    	    uMTG[i].cSUBJECT = cBUFF
    	    IF((LENGTH_ARRAY(cBUFF) > 0) && LEFT_STRING(cBUFF, 1) == $2C || LEFT_STRING(cBUFF, 1) == $00)
    		SET_LENGTH_ARRAY(uMTG[i].cHOST_NAME, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cSTART_DATE, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cSTART_HOUR, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cSTART_MINUTE, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cEND_HOUR, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cEND_MINUTE, 0)
    		SET_LENGTH_ARRAY(uMTG[i].cSUBJECT, 0)
    DEFINE_FUNCTION fnWRITE_FILE_MTG(CHAR cFILENAME[])
        LOCAL_VAR SLONG slFILE_VAR
        LOCAL_VAR INTEGER i
        LOCAL_VAR SLONG slRESULT
        slFILE_VAR = FILE_OPEN(cFILENAME, FILE_RW_NEW)
        IF(slFILE_VAR > 0)
    	    cBUFF = "uMTG[i].cHOST_NAME,',',uMTG[i].cSTART_DATE,',',uMTG[i].cSTART_HOUR,',',uMTG[i].cSTART_MINUTE,',',uMTG[i].cEND_HOUR,',',uMTG[i].cEND_MINUTE,',',uMTG[i].cSUBJECT"
    	    slRESULT = FILE_WRITE_LINE(slFILE_VAR,cBUFF,LENGTH_ARRAY(cBUFF))
    	    SEND_STRING 0, "slRESULT"
    	FILE_CLOSE(slFILE_VAR)
    	SEND_STRING 0,"'GOOD FILE CLOSED ',ITOA(FILE_CLOSE(slFILE_VAR))"
        ELSE
    	SEND_STRING 0,"'BAD FILE OPEN ',ITOA(FILE_CLOSE(slFILE_VAR))"
    (*                STARTUP CODE GOES BELOW                  *)
    TIMELINE_CREATE(TL_FEEDBACK,  nTIMER,  1, TIMELINE_ABSOLUTE, TIMELINE_REPEAT) //Half Second
    TIMELINE_CREATE(TL_FEEDBACK2, nTIMER2, 1, TIMELINE_ABSOLUTE, TIMELINE_REPEAT) // 5 Seconds
    TIMELINE_CREATE(TL_FEEDBACK3, nTIMER3, 1, TIMELINE_ABSOLUTE, TIMELINE_REPEAT) //60 Seconds
    (*                THE EVENTS GO BELOW                      *)
    DATA_EVENT[dvMaster] //Master Data Event
        ONLINE:
    	SEND_COMMAND dvTP, "'ADBEEP'" //When online, BEEP!
    DATA_EVENT[dvTP]
        STRING:
    	STACK_VAR INTEGER x
    	SEND_STRING 0, "'FROM TP: ', DATA.TEXT"
    	SELECT
    	    ACTIVE(FIND_STRING(DATA.TEXT, 'Button 16-', 1)):
    		REMOVE_STRING(DATA.TEXT, 'Button 16-', 1)
    		cBADGE = DATA.TEXT
    		IF(LENGTH_ARRAY(cBADGE == 11))
    		    fnRead_BadgeID('Badge_IDs.csv')
    		    FOR(x=1; x<=MAX_LENGTH_ARRAY(uUSERS); x++)
    			IF(cBADGE == uUSERS[x].cID)
    			    SEND_COMMAND dvTP, "'@PPN-New Mtg'"
    			    SEND_COMMAND dvTP, "'@PPK-Authorization'"
    			    SEND_COMMAND dvTP, "'@PPK-Invalid Entry'"
    			    SEND_COMMAND dvTP_Mtg, "'^TXT-1,0,',uUSERS[x].cFIRST_NAME,',',uUSERS[x].cLAST_NAME"
    			    ON[nVALID_ENTRY]
    			    cHOST_NAME = "uUSERS[x].cFIRST_NAME,' ',uUSERS[x].cLAST_NAME"
    			    SEND_COMMAND dvTP_Mtg, "'^TXT-2,0,',DATE"
    			    BREAK;
    			ELSE
    			    SEND_COMMAND dvTP, "'@PPN-Invalid Entry'"
    			    OFF[nVALID_ENTRY]
    			    WAIT 40
    				SEND_COMMAND dvTP, "'PAGE-Locked'"
    	    ACTIVE(FIND_STRING(DATA.TEXT, '@PPF-Authorization;Locked', 1)):
    		SEND_COMMAND dvTP_Mtg, "'^TXT-3,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-4,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-5,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-6,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-11,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-12,0,'"
    		SEND_COMMAND dvTP_Mtg, "'^TXT-13,0,'"
    	    ACTIVE(FIND_STRING(DATA.TEXT,'KEYB-',1)):
    		REMOVE_STRING(DATA.TEXT,'KEYB-',1)
    		cDATA = DATA.TEXT
    	    ACTIVE(FIND_STRING(DATA.TEXT,'KEYP-',1)):
    		REMOVE_STRING(DATA.TEXT,'KEYP-',1)
    		IF(nTIME == 1)
    		    nHOUR = ATOI(DATA.TEXT)
    		ELSE IF(nTIME == 2)
    		    nMINUTE = ATOI(DATA.TEXT)
    		ELSE IF(nTIME == 3)
    		    nHOUR2 = ATOI(DATA.TEXT)
    		ELSE IF(nTIME == 4)
    		    nMINUTE2 = ATOI(DATA.TEXT)
    	PULSE[nDONE]
    BUTTON_EVENT[dvTP_Mtg, 3]
    	TO[BUTTON.INPUT]
    	nTIME = 1;
        RELEASE:
    	WAIT_UNTIL(nDONE)
    	    cSTART_HOUR = ITOA(nHOUR)
    	    SEND_COMMAND dvTP_Mtg, "'^TXT-3,0,',cSTART_HOUR"
    	    IF(nHOUR >= 8 && nHOUR < 12)
    		SEND_COMMAND dvTP_Mtg, "'^TXT-5,0,AM'"
    	    ELSE
    		SEND_COMMAND dvTP_Mtg, "'^TXT-5,0,PM'"
    BUTTON_EVENT[dvTP_Mtg, 4]
    	nTIME = 2;
        RELEASE:
    	WAIT_UNTIL(nDONE)
    	    cSTART_MINUTE = ITOA(nMINUTE)
    	    IF(nMINUTE == 0)
    		cSTART_MINUTE = "'00'"
    	    SEND_COMMAND dvTP_Mtg, "'^TXT-4,0,',cSTART_MINUTE"
    BUTTON_EVENT[dvTP_Mtg, 11]
    	nTIME = 3;
        RELEASE:
    	WAIT_UNTIL(nDONE)
    	    cEND_HOUR = ITOA(nHOUR2)
    	    SEND_COMMAND dvTP_Mtg, "'^TXT-11,0,',cEND_HOUR"
    	    IF(nHOUR2 >= 8 && nHOUR2 < 12)
    		SEND_COMMAND dvTP_Mtg, "'^TXT-13,0,AM'"
    	    ELSE
    		SEND_COMMAND dvTP_Mtg, "'^TXT-13,0,PM'"
    BUTTON_EVENT[dvTP_Mtg, 12]
    	nTIME = 4;
        RELEASE:
    	WAIT_UNTIL(nDONE)
    	    cEND_MINUTE = ITOA(nMINUTE2)
    	    IF(nMINUTE2 == 0)
    		cEND_MINUTE = "'00'"
    	    SEND_COMMAND dvTP_Mtg, "'^TXT-12,0,',cEND_MINUTE"
    BUTTON_EVENT[dvTP_Mtg, 6]
        RELEASE:
    	WAIT_UNTIL(nDONE)
    	    cSUBJECT = cDATA
    	    SEND_COMMAND dvTP_Mtg, "'^TXT-6,0,',cSUBJECT"
    BUTTON_EVENT[dvTP_Mtg, 10] //reserve a new meeting
    	LOCAL_VAR INTEGER x
    	LOCAL_VAR INTEGER INDEX
    	LOCAL_VAR INTEGER nDURATION
    	LOCAL_VAR INTEGER nNUM_MTGS
    	LOCAL_VAR INTEGER ACCESS
    	INDEX = fnPROCESS_TIME(nHOUR, nMINUTE)
    	nDURATION = fnCONVERT_REQUEST(nHOUR, nMINUTE, nHOUR2, nMINUTE2)
    	nNUM_MTGS = (nDURATION/15)
    	ACCESS = fnPROCESS_REQUEST(INDEX, nNUM_MTGS)
    	IF(LENGTH_ARRAY(cSUBJECT) > 0)
    	    OFF[dvTP_Mtg, 16]
    	    IF(ACCESS == 1)
    		FOR(x=1; x<=nNUM_MTGS; x++)
    		    uMTG[INDEX].cHOST_NAME    = cHOST_NAME
    		    uMTG[INDEX].cSTART_DATE   = DATE
    		    uMTG[INDEX].cSTART_HOUR   = cSTART_HOUR
    		    uMTG[INDEX].cSTART_MINUTE = cSTART_MINUTE
    		    uMTG[INDEX].cEND_HOUR     = cEND_HOUR
    		    uMTG[INDEX].cEND_MINUTE   = cEND_MINUTE
    		    uMTG[INDEX].cSUBJECT      = cSUBJECT
    		    INDEX++
    		    IF(x > nNUM_MTGS)
    			BREAK;
    		fnWRITE_FILE_MTG('New_Mtg.csv')
    		SEND_COMMAND dvTP, "'@PPX-New Mtg'"
    	    ELSE IF(ACCESS == 0)
    		SEND_COMMAND dvTP, "'@PPN-Error'"
    	ELSE
    	    ON[dvTP_Mtg, 16]
    BUTTON_EVENT[dvTP, 4] //Cancel the current meeting
    	LOCAL_VAR INTEGER i
    	LOCAL_VAR INTEGER nDURATION2
    	LOCAL_VAR INTEGER nNUM_MTGs2
    	LOCAL_VAR INTEGER nLINE
    	nLINE = fnPROCESS_TIME(nCURRENT_HOUR, nCURRENT_MIN)
    	nDURATION2 = fnCONVERT_REQUEST(ATOI(uMTG[nLINE].cSTART_HOUR), ATOI(uMTG[nLINE].cSTART_MINUTE), ATOI(uMTG[nLINE].cEND_HOUR), ATOI(uMTG[nLINE].cEND_MINUTE))
    	nNUM_MTGs2 = (nDURATION2/15)
    	FOR(i=1; i<=nNUM_MTGS2; i++)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cHOST_NAME, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cSTART_DATE, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cSTART_HOUR, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cSTART_MINUTE, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cEND_HOUR, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cEND_MINUTE, 0)
    	    SET_LENGTH_ARRAY(uMTG[nLINE].cSUBJECT, 0)
    	    nLINE++
    	    IF(i > nNUM_MTGs2)
    		BREAK;
    BUTTON_EVENT[dcMTGs]
    	STACK_VAR INTEGER BIC
    	BIC = BUTTON.INPUT.CHANNEL
    	ON[dvTP, 6]
    	ON[dvTP, 7]
    	IF(LENGTH_ARRAY(uMTG[BIC].cSUBJECT) > 0)
    	    SEND_COMMAND dvTP, "'^TXT-2,0,',uMTG[BIC].cSUBJECT,' ',uMTG[BIC].cSTART_HOUR,':',uMTG[BIC].cSTART_MINUTE,' - ',uMTG[BIC].cEND_HOUR,':',uMTG[BIC].cEND_MINUTE"
    	ELSE
    	    SEND_COMMAND dvTP, "'^TXT-2,0,Meeting room vacant'"
    	WAIT 50
    	    OFF[dvTP, 6]
    	    OFF[dvTP, 7]
    BUTTON_EVENT[dvTP, 3]
    	STACK_VAR INTEGER y
    	y = fnPROCESS_TIME(nCURRENT_HOUR, nCURRENT_MIN)
    	IF(LENGTH_ARRAY(uMTG[y].cSUBJECT) > 0)
    	    SEND_COMMAND dvTP, "'^TXT-3,0,',uMTG[y].cSUBJECT"
    	ELSE
    	    SEND_COMMAND dvTP, "'^TXT-3,0,There is no meeting to cancel...'"
    TIMELINE_EVENT[TL_FEEDBACK]
        nCURRENT_HOUR = TIME_TO_HOUR(TIME)
        nCURRENT_MIN =  TIME_TO_MINUTE(TIME)
    TIMELINE_EVENT[TL_FEEDBACK2]
        nCURRENT_MEETING = fnFILL_CALENDAR(nCURRENT_HOUR, nCURRENT_MIN)
    TIMELINE_EVENT[TL_FEEDBACK3]
       fnREAD_FILE_MTG('New_Mtg.csv')
    (*            THE ACTUAL PROGRAM GOES BELOW                *)
    DEFINE_PROGRAM
    [dvTP, 1] = (nCURRENT_MEETING == 1)
    (*                     END OF PROGRAM                      *)
    (*        DO NOT PUT ANY CODE BELOW THIS COMMENT           *)
    Ah, completely missed this the other day. Your last call to remove string where you are populating subject is likely returning nothing. When remove_string(..) is called, if the sequence is not found it will return an empty string.
    Unless you have trailing comma's you may have more luck replacing:
    with
    Alternatively, the explode(..) function I pointed to earlier in the thread may be able to neaten things up a bit.
  • PhreaK wrote: »
    with
    Kim,
    thank you... that is exactly what is happening. I was able to write my own function to clean up the commas and blank spaces before I saw the explode function!
  • PhreaK wrote: »
    sorry for the delay:
    DEFINE_TYPE
        CHAR cHOST_NAME[25]
        CHAR cSTART_HOUR[4]
        CHAR cEND_HOUR[4]
        CHAR cEND_MINUTE[4]
        CHAR cSUBJECT[50]
    VOLATILE _sMTG uMTG[MAX_MEETINGS]
    DEFINE_CONSTANT
    MAX_MEETINGS = 36
