NI-3100 + TCP/IP Client
Hello everyone,
I have some troubles with connection to TCP/IP Client by NI-3100.
The aim is to control IP-Camera (Pansonic AW-HE50SE) by sending telenet-string through NI-3100.
NI-3100's IP : 192.168.0.81
Panasonic's IP: 192.168.0.247
1. First of all I established connection with NI-3100 by Ethernet.
2. Secondly, I added this code into standart NetLinx Source File:
But when I send command
the telnet responce is:
The data-indicator on controller shows only INPUT data, but not OUTPUT.
Hope you can help me to find the solution of this problem.
DEFINE_DEVICE dvPAN = 0:3:0 ~~~~~ DEFINE_START IP_CLIENT_OPEN(3,'192.168.0.247',80,IP_TCP)3. Thirdly, I compiled workspace, built Project and System, and transfered two files (*.tkn and *.src) to NI-3100.
send_string dvPAN, "'%command%'"
Device Name dvPAN is invalid
Are you s?re your connection is open?
Use data-event online/offline to confirm it.
DATA_EVENT[dvIPDevice]
ONLINE:
SEND_STRING 0, 'IP Device ON-LINE'
WAIT 100
<things to do when device comes on line>
OFFLINE:
SEND_STRING 0, 'IP Device OFF-LINE'
ONERROR:
SEND_STRING 0, 'IP Device ERROR'
SEND_STRING 0, "ITOA(DATA.NUMBER)"
<IP_CLIENT_OPEN can run here to reestablish comm>
Then you can get an idea what is happening.
I've never used a wait before sending once getting the online notification, with http you usually have 30 seconds before the server will drop the connection so a 10 second wait should be alright just not nescassary. I'd get rid of it since the quicker you send the sooner you can send your next command and 10 seconds is a long time to hold things up.
That wait was to "do other things" after the device comes online. This was a device specific thing I just left in my generic example.
I will check it in 5 mins.
It would be great! Can you send me link or archive/file in PM?
Also, you can share it here, but I don't know is it allowed or not.
I tried that:
DEFINE_EVENT DATA_EVENT[dvPan] { ONLINE: { SEND_STRING 0, 'IP Device ON-LINE' } OFFLINE: { SEND_STRING 0, 'IP Device OFF-LINE' } ONERROR: { SEND_STRING 0, 'IP Device ERROR' SEND_STRING 0, "ITOA(DATA.NUMBER)" IP_CLIENT_OPEN(3,'192.168.0.247',80,IP_TCP) } }But after master reboot there is nothing in Diagnostic and Notifications dialogs.
Where should this messages (SEND_STRING) be showed?
That's all. So there is nothing about the message we send.
Should IP-Device be showed in tree-list?
​ SEND_STRING 0, 'IP Device ERROR' SEND_STRING 0, "ITOA(DATA.NUMBER)"note: that I didn't include the ip_client_open here because that will usually screw up the master, oprening, error, opening, error, etc forever, usually you can attempt to re-open after a 30+ second delay based on the error number, most errors you just send a notifications and don't attempt to re connect.So in your diagnostic print out you should have seen your send_string 0 if you have one in your onerror handler and if your did you would see the error number and that would help to know what the problem is. Verify the camera port, IP and it's protocol, TCP or UDP. Also you should move the IP_CLIENT_OPEN out of define start and and put it under a button push or something so you can fire it when you're ready to observe the diagnostics.
No, your IP devices won't show up in the tree, only AMX devices.
First I will create a CALL:
DEFINE_CALL 'dvPan_Start'
SEND_STRING 0,'dvPan_Start CALLED'
IP_CLIENT_OPEN(dvPan.port,'192.168.0.247',80,IP_TCP)
Then you can use this when master comes online to start communications and in an error event or button event to restart communications
DATA_EVENT [dvMASTER]
ONLINE:
WAIT 100
CALL 'dvPan_Start'
Plus this will give you time to get through lots of the master booting messages.
In this instance I think the OP should make some global variable for all his values and in a button push or even after a flag variable in define_program call his IP_CLIEN_OPEN so he can change the parameters on the fly. Port number, IP address, UPD/TCP and then in the debug window change the variables and then set his flag making sure that he immediately 0's that flag. In diagnostics watch what happens. Posting a link to the camera's api might help too so we can take a gander for ourselves.
Yeap, it would be great!
Also, I connected all the devices to another NI-3100. And that's it. Everything is working. Thank you!
There are some problems with first NI-3100, maybe.
In TP4 I noticed that there is a function called "Recieve from Panel". What does it mean? So can I recieve the compiled project and recover it?
Also, I have an old compiled project in NetLinx. Can I recover old project from NI-3100 without source code?
Thank you
Well, you can recover them in the sense that you can save the file and reinstall it if need be. But, without source, you cannot open/modify it in Netlinx Studio.
DEFINE_DEVICE dvcam201 = 0:26:0 //Cam 1 dvcam202 = 0:27:0 //Cam 2 dvcam203 = 0:28:0 //Cam 3 dvcam204 = 0:29:0 //Cam 4 dvcam205 = 0:30:0 //Cam 5 DEFINE_START //NOTE: device definition values are actually in an include file in place here, this is just one sample rm[1].d[26].status = 1 //ONLINE rm[1].d[26].dbid = 0 // rm[1].d[26].type = 7 //Panasonic Camera rm[1].d[26].commtype = 2 //IP rm[1].d[26].kind = "'c'" //Camera rm[1].d[26].c = 1 //Camera ID rm[1].d[26].name = "'Cam1'" rm[1].d[26].ipcomm[1].ipaddr = "'10.1.20.16'" rm[1].d[26].ipcomm[1].ipport = 80 rm[1].d[26].ipcomm[1].devid = dvcam201 for(tmp_idx1 = 1; tmp_idx1 <= 2; tmp_idx1++ ) { for(tmp_idx2 = 1; tmp_idx2 <= 32; tmp_idx2++) { //COMM DEVICE INITIALIZATION call 'debug' ("'INIT FOR Loop: RM:',itoa(tmp_idx1),'-',itoa(rm[tmp_idx1].status),' DID:',itoa(tmp_idx2),'-',itoa(rm[tmp_idx1].d[tmp_idx2].status),' COMMTYPE:',itoa(rm[tmp_idx1].d[tmp_idx2].commtype)") rm[tmp_idx1].d[tmp_idx2].buffout = "" //clear buffers on boot rm[tmp_idx1].d[tmp_idx2].buffin = "" //clear buffers on boot if(rm[tmp_idx1].status==1 && rm[tmp_idx1].d[tmp_idx2].status==1 && rm[tmp_idx1].d[tmp_idx2].commtype==2 ) { //Room is online, Device is online, Device is IP based call 'debug' ("'Opening Device: Room:',itoa(tmp_idx1),' Device:',itoa(tmp_idx2),' DevPort:',itoa(rm[tmp_idx1].d[tmp_idx2].ipcomm[1].devid.port),' IP:',rm[tmp_idx1].d[tmp_idx2].ipcomm[1].ipaddr,' IPPort:',itoa(rm[tmp_idx1].d[tmp_idx2].ipcomm[1].ipport)") ip_client_open(rm[tmp_idx1].d[tmp_idx2].ipcomm[1].devid.port,rm[tmp_idx1].d[tmp_idx2].ipcomm[1].ipaddr,rm[tmp_idx1].d[tmp_idx2].ipcomm[1].ipport,IP_TCP) } } } DATA_EVENT data_event[d_all] { //IP Based Devices onerror: { //generally only IP devices will have errors stack_var integer this_dev stack_var integer this_port stack_var integer this_rm stack_var integer this_did stack_var integer this_a stack_var integer this_c stack_var integer this_j stack_var integer this_p stack_var integer this_s stack_var integer this_v this_dev = data.device.number if(this_dev > 40 && this_dev < 100) { //Axcent slave, move DEV to PORT this_port = this_dev } else { this_port = data.device.port } this_rm = rlookup[this_port].rm this_did = rlookup[this_port].d this_a = rlookup[this_port].a this_c = rlookup[this_port].c this_j = rlookup[this_port].j this_p = rlookup[this_port].p this_s = rlookup[this_port].s this_v = rlookup[this_port].v call 'debug' ("'DATA EVENT - ERROR - Data.Device: Raw:',itoa(data.device.number),' Managed:',ITOA(this_dev)") call 'debug' ("'Data.Device.Port: Raw:',itoa(data.device.port),' Managed:',ITOA(this_port)") call 'debug' ("'DID:',itoa(this_did),' Aud:',itoa(this_a),' Cam:',ITOA(this_c),' Joy:',ITOA(this_j),' Proj:',ITOA(this_p),' Swt:',ITOA(this_s),' VC:',ITOA(this_v)") call 'debug' ("'Port error: RM:',itoa(this_rm),' DID:',itoa(this_did),' ERROR=',ITOA(Data.Number)") rm[this_rm].d[this_did].errorcount++ call 'debug' ("'Error Count: ',itoa(rm[this_rm].d[this_did].errorcount)") if(data.number!=14&&rm[this_rm].d[this_did].errorcount<10) { // 14 is "port already open" if(!timeline_active((this_rm*1000)+(this_did*10)+5)) { call 'debug' ("'Starting Delayed Port Re-Open Sequence. ErrorCount:',itoa(rm[this_rm].d[this_did].errorcount)") timeline_create((this_rm*1000)+(this_did*10)+5,cmd[rm[this_rm].d[this_did].type].commtimeout,1,timeline_absolute,timeline_once) // Delayed Re-Open } else { call 'debug' ("'Multiple Port Errors, Delay Re-Open already in progress: RM:',itoa(this_rm),' DID:',itoa(this_did),' ERRORCOUNT',itoa(rm[this_rm].d[this_did].errorcount)") } } else if(data.number!=14&&rm[this_rm].d[this_did].errorcount>10) { call 'debug' ("'Persistent Device Error: RM:',itoa(this_rm),' DID:',itoa(this_did)") call 'debug' ("'Port closed, stays closed, submit trouble ticket'") // ip_client_close(rm[this_rm].d[this_did].ipcomm[1].devid.port) //force close port //call 'submittroubleticket' (this_rm,"'system'") } } online: { //All devices come online stack_var integer this_dev stack_var integer this_port stack_var integer this_rm stack_var integer this_did stack_var integer this_a stack_var integer this_c stack_var integer this_j stack_var integer this_p stack_var integer this_s stack_var integer this_v call 'debug' ("'PRE-LOAD DATA: DID:',itoa(this_did),' Aud:',itoa(this_a),' Cam:',ITOA(this_c),' Joy:',ITOA(this_j),' Proj:',ITOA(this_p),' Swt:',ITOA(this_s),' VC:',ITOA(this_v)") this_dev = data.device.number if(this_dev > 40 && this_dev < 100) { //Axcent slave, move DEV to PORT this_port = this_dev } else { this_port = data.device.port } this_rm = rlookup[this_port].rm this_did = rlookup[this_port].d this_a = rlookup[this_port].a this_c = rlookup[this_port].c this_j = rlookup[this_port].j this_p = rlookup[this_port].p this_s = rlookup[this_port].s this_v = rlookup[this_port].v call 'debug' ("'DATA EVENT - ONLINE - Data.Device: Raw:',itoa(data.device.number),' Managed:',ITOA(this_dev)") call 'debug' ("'DATA EVENT - ONLINE - Data.Device.Port: Raw:',itoa(data.device.port),' Managed:',ITOA(this_port)") call 'debug' ("'RLOOKUP DATA: DID:',itoa(this_did),' Aud:',itoa(this_a),' Cam:',ITOA(this_c),' Joy:',ITOA(this_j),' Proj:',ITOA(this_p),' Swt:',ITOA(this_s),' VC:',ITOA(this_v)") rm[this_rm].d[this_did].errorcount = 0 call 'debug' ("'Error Count: ',itoa(rm[this_rm].d[this_did].errorcount)") call 'debug' ("'DEVICE ONLINE: RM:',itoa(this_rm),' DID:',itoa(this_did)") select { active(rm[this_rm].d[this_did].commtype==1): { //Serial Device call 'debug' ("'Setting Serial Parameters for device: RM:',itoa(this_rm),' DID:',itoa(this_did)") send_command data.device,"rm[this_rm].d[this_did].sercomm" } active(rm[this_rm].d[this_did].commtype==2): { //IP Device call 'debug' ("'IP Device Online:',itoa(this_rm),' DID:',itoa(this_did),' Send appropriate initialization strings...'") } active(rm[this_rm].d[this_did].commtype==3): { //IR Device call 'debug' ("'Setting IR CTON/CTOFF: RM:',itoa(this_rm),' DID:',itoa(this_did)") SEND_COMMAND DATA.DEVICE, "'CTON',2" SEND_COMMAND DATA.DEVICE, "'CTOF',2" } active(1): { //UN-TRAPPED ONLINE EVENT call 'debug' ("'UNTRAPPED DEVICE ONLINE EVENT:',itoa(this_rm),' DID:',itoa(this_did)") } } select { active(this_a>0): { //Audio Device call 'debug' ("'Audio device online: RM:',itoa(this_rm),' DID:',itoa(this_did),' AudioID:',itoa(this_a)") } active(this_c>0): { //Camera Device call 'debug' ("'Camera Control Session Established: RM:',itoa(this_rm),' DID:',itoa(this_did),' CamID:',itoa(this_c)") call 'debug' ("'Setting IPCONNECT Value'") rm[this_rm].d[this_did].ipconnect = 1 } active(this_p>0&&rm[this_rm].d[this_did].type==2): { //EPSON Projector call 'debug' ("'Projector coming online: RM:',itoa(this_rm),' DID:',itoa(this_did),' projID:',itoa(this_p)") call 'debug' ("'EPSON Projector, Sending Connect Header: ','ESC/VP.net',$10,$03,$00,$00,$00,$00") SEND_STRING rm[this_rm].d[this_did].ipcomm[1].devid,"'ESC/VP.net',$10,$03,$00,$00,$00,$00" rm[this_rm].d[this_did].buffout = "''" // clear command buffer call 'addcmd' (this_rm,this_did,cmd_pwrq) timeline_create(((this_rm*1000)+(this_did*10)+1),cmd[rm[this_rm].d[this_did].type].polltime,1,timeline_absolute,timeline_repeat) //once-per-minute display auto-power check } active(this_j>0): { //Joystick Online call 'debug' ("'Joystick coming online: RM:',itoa(this_rm),' DID:',itoa(this_did),' JoyID:',itoa(this_j)") } active(this_p>0): { //other display call 'debug' ("'Non-epson display device online: RM:',itoa(this_rm),' DID:',itoa(this_did),' ProjID:',itoa(this_p)") } active(this_s>0): { //Switch Online call 'debug' ("'Switch coming online: RM:',itoa(this_rm),' DID:',itoa(this_did),' SwtID:',itoa(this_s)") } active(this_v>0): { //POLYCOM Online call 'debug' ("'Polycom coming online: RM:',itoa(this_rm),' DID:',itoa(this_did),' PolyID:',itoa(this_v)") } active(1): { //fall-thru call 'debug' ("'FALL-THRU TRAP Device Online: RM:',itoa(this_rm),' DID:',itoa(this_did)") } } } offline: { stack_var integer this_dev stack_var integer this_port stack_var integer this_rm stack_var integer this_did stack_var integer this_a stack_var integer this_c stack_var integer this_j stack_var integer this_p stack_var integer this_s stack_var integer this_v this_dev = data.device.number if(this_dev > 40 && this_dev < 100) { //Axcent slave, move DEV to PORT this_port = this_dev } else { this_port = data.device.port } this_rm = rlookup[this_port].rm this_did = rlookup[this_port].d this_a = rlookup[this_port].a this_c = rlookup[this_port].c this_j = rlookup[this_port].j this_p = rlookup[this_port].p this_s = rlookup[this_port].s this_v = rlookup[this_port].v call 'debug' ("'DATA EVENT - OFFLINE - Data.Device: Raw:',itoa(data.device.number),' Managed:',ITOA(this_dev)") call 'debug' ("'Data.Device.Port: Raw:',itoa(data.device.port),' Managed:',ITOA(this_port)") call 'debug' ("'DID:',itoa(this_did),' Aud:',itoa(this_a),' Cam:',ITOA(this_c),' Joy:',ITOA(this_j),' Proj:',ITOA(this_p),' Swt:',ITOA(this_s),' VC:',ITOA(this_v)") call 'debug' ("'Port error: RM:',itoa(this_rm),' DID:',itoa(this_did),' ERROR=',ITOA(Data.Number)") rm[this_rm].d[this_did].errorcount++ call 'debug' ("'Error Count: ',itoa(rm[this_rm].d[this_did].errorcount)") if(data.number!=14&&rm[this_rm].d[this_did].errorcount<10&&rm[this_rm].d[this_did].c==0) { // 14 is "port already open" if(!timeline_active((this_rm*1000)+(this_did*10)+5)) { call 'debug' ("'Starting Delayed Port Re-Open Sequence. ErrorCount:',itoa(rm[this_rm].d[this_did].errorcount)") timeline_create((this_rm*1000)+(this_did*10)+5,cmd[rm[this_rm].d[this_did].type].commtimeout,1,timeline_absolute,timeline_once) // Delayed Re-Open } else { call 'debug' ("'Multiple Port Errors, Delay Re-Open already in progress: RM:',itoa(this_rm),' DID:',itoa(this_did),' ERRORCOUNT',itoa(rm[this_rm].d[this_did].errorcount)") } } else if(rm[this_rm].d[this_did].c==1) { call 'debug' ("'Camera Port Closing (NORMAL): RM:',itoa(this_rm),' DID:',itoa(this_did),' Cam:',itoa(this_c)") // call 'debug' ("'Port Remains Closed for Device RM:',itoa(this_rm),' DID:',itoa(this_did)") } else if(data.number!=14&&rm[this_rm].d[this_did].errorcount>10) { call 'debug' ("'Persistent Device Error: RM:',itoa(this_rm),' DID:',itoa(this_did)") call 'debug' ("'Port Remains Closed for Device RM:',itoa(this_rm),' DID:',itoa(this_did)") } select { active(this_c>0): { //Camera Device call 'debug' ("'Camera Control Session Complete: RM:',itoa(this_rm),' DID:',itoa(this_did),' CamID:',itoa(this_c)") call 'debug' ("'Clearing IPCONNECT Value'") rm[this_rm].d[this_did].ipconnect = 0 } } } string: { stack_var integer this_dev stack_var integer this_port stack_var integer this_rm stack_var integer this_did stack_var integer this_a stack_var integer this_c stack_var integer this_j stack_var integer this_p stack_var integer this_s stack_var integer this_v this_dev = data.device.number if(this_dev > 40 && this_dev < 100) { //Axcent slave, move DEV to PORT this_port = this_dev } else { this_port = data.device.port } this_rm = rlookup[this_port].rm this_did = rlookup[this_port].d this_a = rlookup[this_port].a this_c = rlookup[this_port].c this_j = rlookup[this_port].j this_p = rlookup[this_port].p this_s = rlookup[this_port].s this_v = rlookup[this_port].v call 'debug' ("'DATA EVENT - STRING - Data.Device: Raw:',itoa(data.device.number),' Managed:',ITOA(this_dev)") call 'debug' ("'Data.Device.Port: Raw:',itoa(data.device.port),' Managed:',ITOA(this_port)") call 'debug' ("'DID:',itoa(this_did),' Aud:',itoa(this_a),' Cam:',ITOA(this_c),' Joy:',ITOA(this_j),' Proj:',ITOA(this_p),' Swt:',ITOA(this_s),' VC:',ITOA(this_v)") call 'debug' ("'Data From Device: RM:',itoa(this_rm),' DID:',itoa(this_did),' Port:',itoa(data.device.port),' - ',data.text") call 'debug' ("'Adding Data to Buffer: RM:',itoa(this_rm),' DID:',itoa(this_did),' Data:',data.text") call 'debug' ("'Buffer Before:',rm[this_rm].d[this_did].buffin") rm[this_rm].d[this_did].buffin = "rm[this_rm].d[this_did].buffin,data.text" call 'debug' ("'Buffer After:',rm[this_rm].d[this_did].buffin") } } //Camera control button_event[dvtp_camera,btnset_cam] { //up push: { stack_var integer this_rm stack_var integer this_did stack_var integer this_btn stack_var integer this_c this_rm = tprm(button.input.device.number) this_c = rm[this_rm].p[11].feed - 8 /// gets current camera selection this_did = rm[this_rm].c[this_c].did /// gets current camera DID this_btn = button.input.channel call 'debug' ("'Camera Push Control: RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") select { active(this_btn==1): { call 'debug' ("'Tilt Up (Push) RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#T60&res=1'" } active(this_btn==2): { call 'debug' ("'Tilt Down (Push) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#T40&res=1'" } active(this_btn==3): { call 'debug' ("'Pan Left (Push) RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#P40&res=1'" } active(this_btn==4): { call 'debug' ("'Pan Right (Push) RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#P60&res=1'" } active(this_btn==5): { call 'debug' ("'Zoom IN (Push) RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#Z60&res=1'" } active(this_btn==6): { call 'debug' ("'Zoom OUT (Push) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#Z40&res=1'" } active(this_btn==7): { call 'debug' ("'Focus IN (Push) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'F40&res=1'" } active(this_btn==8): { call 'debug' ("'Focus OUT (Push) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#F60&res=1'" } active(this_btn==9): { call 'debug' ("'Auto Focus (Push) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#D1&res=1'" } } call 'debug' ("'Current Buffer: RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_btn),' Buffer:',rm[this_rm].d[this_did].buffout") } hold[11]: { stack_var integer this_rm stack_var integer this_did stack_var integer this_btn stack_var integer this_c this_rm = tprm(button.input.device.number) this_c = rm[this_rm].p[11].feed - 8 /// gets current camera selection this_did = rm[this_rm].c[this_c].did /// gets current camera DID this_btn = button.input.channel call 'debug' ("'Camera Hold Control: RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") select { active(this_btn==1): { call 'debug' ("'Tilt Up (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#T90&res=1'" } active(this_btn==2): { call 'debug' ("'Tilt Down (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#T10&res=1'" } active(this_btn==3): { call 'debug' ("'Pan Left (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#P10&res=1'" } active(this_btn==4): { call 'debug' ("'Pan Right (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#P90&res=1'" } active(this_btn==5): { call 'debug' ("'Zoom IN (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#Z90&res=1'" } active(this_btn==6): { call 'debug' ("'Zoom OUT (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#Z10&res=1'" } active(this_btn==7): { call 'debug' ("'Focus IN (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#F10&res=1'" } active(this_btn==8): { call 'debug' ("'Focus OUT (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#F90&res=1'" } active(this_btn==9): { call 'debug' ("'Auto Focus (Hold) RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#D1&res=1'" } } call 'debug' ("'Current Buffer: RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_btn),' Buffer:',rm[this_rm].d[this_did].buffout") } release: { stack_var integer this_rm stack_var integer this_did stack_var integer this_btn stack_var integer this_c this_rm = tprm(button.input.device.number) this_c = rm[this_rm].p[11].feed - 8 /// gets current camera selection this_did = rm[this_rm].c[this_c].did /// gets current camera DID this_btn = button.input.channel call 'debug' ("'Camera Release Control: RM:',itoa(this_rm),' DID:',itoa(this_did),' CAM:',itoa(this_c),' Btn:',itoa(this_btn)") select { active(this_btn==1||this_btn==2): { //stop all tilt call 'debug' ("'STOP Tilt RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#T50&res=1'" } active(this_btn==3||this_btn==4): { //stop all pan call 'debug' ("'STOP Pan RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#P50&res=1'" } active(this_btn==5||this_btn==6): { //stop all zoom call 'debug' ("'STOP Zoom RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#Z50&res=1'" } active(this_btn==7||this_btn==8): { //stop all focus call 'debug' ("'STOP Focus RM:',itoa(this_rm),' CAM:',itoa(this_did),' Btn:',itoa(this_btn)") rm[this_rm].d[this_did].buffout = "rm[this_rm].d[this_did].buffout,'#F50&res=1'" } } } } DEFINE_PROGRAM //Cams RM 2 while(find_string(rm[2].d[26].buffout,"'res=1'",1)&&!timeline_active(2263)) { //command in buffer timeline_create(2263,cmd[rm[2].d[26].type].commtimeout,1,timeline_absolute,timeline_once) // response limit timer144 // call 'debug' ("'Processing Camera Control Command RM:2 DID:26 CAM:1 Buffer:',rm[2].d[26].buffout") rm[2].d[26].ipdone = 0 rm[2].d[26].lastacmd = remove_string(rm[2].d[26].buffout,"'res=1'",1) ip_client_open( rm[2].d[26].ipcomm[1].devid.port , rm[2].d[26].ipcomm[1].ipaddr , 80,1)//80=port,1=TCP call 'debug' ("'Opening Campera IP Connection...'") wait_until(rm[2].d[26].ipconnect==1) { //set to 1 in online data event, 0 in offline event send_string rm[2].d[26].ipcomm[1].devid,"'GET /cgi-bin/aw_ptz?cmd=#',rm[2].d[26].lastacmd,$0D,$0A" // call 'debug' ("'Cam Command Submit: ','GET /cgi-bin/aw_ptz?cmd=#',rm[2].d[26].lastacmd,$0D,$0A") } } while( length_string( rm[2].d[26].buffin ) > 0 && rm[2].d[26].ipconnect == 0 ) { // call 'debug' ("'Cam Response Processing, Original Command: ', rm[2].d[26].lastacmd ") call 'camresponseparser' ( 2, 26, "rm[2].d[26].buffin" ) rm[2].d[26].buffin = "''" rm[2].d[26].ipdone = 1 timeline_kill(2263) // }If you've got questions about the code, I'll do my best to explain.That's 2...
1. Yes. As the onboard HELP in TPDesign will explain. You connect to the panel, click that button, and pick the filename and location. And the result is completely editable.
2. As Eric says, all you can get is what's in it... if there is no source code loaded in the NI, you can only get the TKN for reuse, not editable.
To get the TKN, you can't use typical FTP clients, as the stored program "prog.tkn' is in a hidden folder.
Open a command (DOS) window... here's a session: YOUR INPUT IS BOLD and explanation is in green italic (don't type the explanation into the session!)
Microsoft Windows [Version 6.1.7601]
Copyright (c) 2009 Microsoft Corporation. All rights reserved.
C:\Users\John.Junior>ftp 192.168.1.201 [you type ftp and the IP of the NetLinx]
Connected to 192.168.1.201.
220 VxWorks (VxWorks 6.3) FTP server ready
User (192.168.1.201 : (none)): administrator [user and password of the NI. Default is "administrator" and "password"]
331 Password required
Password: [password does not echo]
230 User logged in
ftp> binary [set mode by typing "binary"]
200 Type set to I, binary mode
ftp> get ../prog.tkn d:/extractedcode.tkn [this is the meat. Choose the location to write the file, here, on the root of D]
200 Port set okay
150 Opening BINARY mode data connection [it can take a minute here... be patient]
226 Transfer complete
ftp: 13874097 bytes received in 6.83Seconds 2032.54Kbytes/sec.
ftp> quit [and.... we're out.]
221 Bye...see you later
As mentioned earlier, HTTP (port 80) should only be opened and closed with each command.
But if you are after TELNET, you can open and maintain the port (in theory).
Anyway, just my two cents. I keep seeing TELNET discussed, but port 80 is not TELNET.
Lastly, this - ///
'the telnet responce is:
Code:
Does not make much sense. The receiving device should never see the text 'dvPAN' (and it certainly can't if you're trying the wrong port).
The text 'dvPAN' is local to the program in Netlinx only. It never gets transmitted (unless it's part of you %command% variable).
Therefore, it has to be Netlinx reporting that error, which would mean the reference (dvPAN) is incorrect.
Bottomline, get on the right port first.. change 80 to 23 if TELNET is what you really want. But if it's HTTP on port 80 that you need, you have a bigger fish to fry.