Data Sharing between controlers
Hi guys
how can I share the data of the statuses between cotrolers?
For example, in the Master that connected to the Lutron lighting system, I will hold a table with the current states of the lighting system (ONLY on this Master)
How will you recommend to share the data beween all home controllers that need to enter to the lighting screen and to fetch the current statuses?
As I see it ths simple way is to make all the relevant lighing screens handling in this controller for all the TP.
But what if now I have some screens that relate to other controller that need to get status from this controller?
I don't want to listen to status change in each controller.
Any tricks for this?
thank
Adys.
  • SOLUTION 1
    Assuming that the second controller isn't meant to change the data on the first controller - the transfer is one-way:
    You could set up a mechanism so that any state change on one controller is immediately replicated to the other. It would be easy to code, assuming limited state volatility wouldn't add excess load, and would be plenty fast.
    Ideally hold the state in a generic format eg an array of integers subscripted by a set of constants. Always update the state indirectly through a routine which also checks for a change of state and sends a notification string (array subscript plus new value) to the other controller. On the other controller accept the string and update an array that mirrors the first.
    This code is of course very reusable. Here is a first draft neither compiled nor tested:
    define_constant
    nStateSize = 1000
    nStateLight1 = 1
    nStateLight2 = 2
    etc
    define_variable
    integer nState[nStateSize]
    define_function integer StateGet(
      integer nArgSubscript)
    return nState[nArgSubscript];
    define_function StateSet(
      integer nArgSubscript,
      integer nArgValue)
    if (nState[nArgSubscript] <> nArgValue)
      nState[nArgSubscript] = nArgValue
      send_string vOtherController,"'STATE',nArgSubscript,nArgValue"
    SOLUTION 2
    Alternatively use one or more virtual devices in the same way. I haven't done this but I believe it works. It would be good to hear from someone who has done it.
    In controller 1, create a virtual device and use its levels and channels as places to store information in the same way that I use the generic repository in the method above. Channels are binary repositories; levels offer values 0-255.
    Master-to-master makes that device and its attributes seamlessly visible on controller 2.
    If you access this device at both ends via a single routine (or two), you can change your mind about it, extend it, or re-implement it very easily. That is, for instance, you can change from solution 1 to 2 without messing with your code.
    This code is also very reusable.
  • I have used solution 2 that NMarkRoberts mentioned. I usually have a fairly large comment section like the one below:
    (* MASTER-TO-MASTER COMMUNICATIONS: THE vdvCOMM VIRTUAL DEVICE POINTS TO THE *)
    (* MASTER IN THIS ROOM. CHANNELS ARE SET TO INDICATE THE STATUS OF VARIOUS *)
    (* OPERATIONS. *)
    (* CHANNEL 1 ON INDICATES THAT A IS IN COMBINED MODE WITH B. *)
    (* CHANNEL 2 ON INDICATES THAT A IS IN COMBINED MODE WITH C. *)
    (* CHANNEL 2 CAN NOT BE ON UNLESS CHANNEL 1 IS ALSO ON. *)
    (* CHANNEL 11 ON INDICATES THAT ROOM B IS IN USE. *)
    (* CHANNEL 12 ON INDICATES THAT ROOM C IS IN USE. *)
    (* ROOM A CONTROLS CHANNELS 1 AND 2. ROOM B CONTROLS CHANNEL 11 AND *)
    (* ROOM C CONTROLS CHANNEL 12. IF SATELLITE ROOMS ARE IN USE INDICATED BY *)
    (* CHANNELS 11 OR 12, THEN A WILL NOT BE ABLE TO ENTER COMBINED MODE WITH *)
    (* THAT ROOM. *)
    (* LEVEL 1 WILL CONTAIN THE VALUE OF THE ROOM CURRENTLY CONTROLING THE VTC *)
    (* LEVEL 2 WILL CONTAIN THE VALUE OF THE ROOM CURRENTLY CONTROLING THE DVD *)
    (* LEVEL 3 WILL CONTAIN THE VALUE OF THE ROOM CURRENTLY CONTROLING THE VCR *)
    (* LEVEL 4 WILL CONTAIN THE VALUE OF THE ROOM CURRENTLY CONTROLING THE WIRELESS *)
    (* MICROPHONES. *)
    (* A VALUE OF 3 INDICATES THAT THE DEVICE IS FREE. *)
    vdvCOMM = 33050:1:201 // INTER-ROOM COMMUNICATION
    This particular application had three rooms, each having a master. The rooms could be combined (0 and 1 or 0 and 1 and 2) or used as separate systems. There are four devices that are shared by the three rooms. These are the Video Conferencing system, the DVD, the VCR, and the wireless mics.
    In the setup of each room, I assign a room number to a persistent variable. For the shared devices, the room that has the device "reserved" sends their room number as the level value for that particular device. When the value is 3, the device is available. If I do it again, I would probably number the rooms 1, 2, and 3 and have the 0 to indicate that the device is available. I don't know where my head was that day.
    Anyway, I use send_level, level_event, channel_event, and so on against this virtual device to maintain the status of the system. Since the device buttons are available on the touch panel in each room, I use the level of a particular device to change the icon on the buttons, so that if room 1 is using the DVD player, the circle and slash symbol appears on the DVD buttons on the touch panels for rooms 0 and 2.
    In other sites, I have also used channels to indicate which lighting preset is currently in use by the main room, so that if the rooms are combined I can tell the Lutron in each system to select the same lighting preset.
    This method is easy to use, and the response is good since you use channel and level events to keep the mutiple systems in sync.
  • adysadys Posts: 395
    thanks guys
    the second solution look good to me too.
    Can anyone give a few words/resource/examples on channels and levels?
    I looked at the programming manuals - very few words on those subjects and I think I miss the basic idea on channels and levels...
    thanks
    Ady
  • If its just simply having a TP push the lighting buttons and show the current LED state of a lighting system on a different system just define that TP on the system where the lighting code exists and program as you would a TP locally.
       dv232_Lights = 5001:1:0 //Lighting control attached to this system
       dvTPA_LIGHTS = 10001:1:0 //Touchpanel attached to this system
       dvTPB_LIGHTS = 10001:1:2 //Touchpanel attached to another system
    DEFINE_CONSTANT
       dvTP_LIGHTS[ ] = {dvTPA_LIGHTS, dvTPB_LIGHTS}
       dvTPBT_LIGHTS[ ]  = {1, 2, 3, 4, 5, 6, 7, 8,, 9, 10}
       dvTPFB_LIGHTS[ ]  = {11,12, 13, 14, 15, 16, 17, 18,, 19, 20}
    BUTTON_EVENT[dvTP_LIGHTS,nTPBT_LIGHTS]
        STACK_VAR iTp, iButton
        iTp = GET_LAST(dvTP_Lights)
        iButton = GET_LAST(nTPBT_LIGHTS)
        TO[BUTTON.INPUT]
        SEND_COMMAND dv232_Lights,"'KBP',ITOA(nRoomLights[iTp],':',ITOA(iButton)"))
    TIMELINE_EVENT[tlTPAFB_LIGHTS]
    TIMELINE_EVENT[tlTPBFB_LIGHTS]
      STACK_VAR iTp, i
      iTp = GET_LONG(TIMELINE.ID,tlTPFB_LIGHTS)
      FOR(i=1,i<=10,i++)
          nTPFB_LIGHTS[iTp][i] = nKpFb_Lights[i]
    Neither compiled nor tested:
    define_variable
    char cState[8]
    device vState
    define_start
    (* Associate cState array with levels *)
    stack_var integer nCounter
    for (nCounter = 1; nCounter<=8; nCounter++)
      create_level vState,nCounter,cState[nCounter]
    define_function integer StateGetBoolean(
      integer nArgSubscript) (* 1..255 *)
    return [vState,nArgSubscript];
    define_function StateSetBoolean(
      integer nArgSubscript, (* 1..255 *)
      integer bArgValue) (* 0,1 *)
    [vState,nArgSubscript] = bArgValue
    define_function char StateGetChar(
      integer nArgSubscript) (* 1..8 *)
    return cState[nArgSubscript];
    define_function StateSetChar(
      integer nArgSubscript, (* 1..8 *)
      char cArgValue) (* 0..255 *)
    send_level vState,nArgSubscript,cArgValue
  • Here is a cut and paste of the code I did to create and use a virtual device to pass info between three masters. It definately will not compile since there are major sections of the boring stuff left out.
    PROGRAM_NAME='Sample'
    (*  FILE CREATED ON: 02/25/2007  AT: 18:39:48              *)
    (*  FILE_LAST_MODIFIED_ON: 02/25/2007  AT: 18:52:37        *)
    (* System Type : NetLinx                                   *)
    (* REV HISTORY:                                            *)
    (*  OPERATIONS.        *)
    (*  THAT ROOM.        *)
    (*  MICROPHONES.        *)
    (*               CONSTANT DEFINITIONS GO BELOW             *)
    DEFINE_CONSTANT
    (*              DATA TYPE DEFINITIONS GO BELOW             *)
    DEFINE_TYPE
    PERSISTENT INTEGER cfgROOMNUM             // 0=A, 1=B, 2=C
    VOLATILE INTEGER nROOM_MODE               // 0= OFF, 1= PRESENTATION, 2= VTC,
                                              // 3= AUDIO ONLY
    VOLATILE INTEGER nCONFIG_MODE             // 0= NORMAL,1=COMBINED W/Room B, 2=COMBINED W/Room B&Room C
    VOLATILE INTEGER nB_STATUS            	  // 0=IDLE, 1=IN USE
    VOLATILE INTEGER nC_STATUS             	  // 0=IDLE, 1=IN USE
    (*               LATCHING DEFINITIONS GO BELOW             *)
    DEFINE_LATCHING
    (*       MUTUALLY EXCLUSIVE DEFINITIONS GO BELOW           *)
    DEFINE_MUTUALLY_EXCLUSIVE
    (*        SUBROUTINE/FUNCTION DEFINITIONS GO BELOW         *)
    DEFINE_FUNCTION ALL_OFF ()
        IF (VTC_STATUS = cfgROOMNUM)
    	SEND_COMMAND vdvTandberg,'HOOK=0:ON'
            SEND_LEVEL vdvCOMM,1,3
        IF (DVD_STATUS = cfgROOMNUM)
            SEND_LEVEL vdvCOMM,2,3
        IF (VCR_STATUS = cfgROOMNUM)
            SEND_LEVEL vdvCOMM,3,3
        IF (WIRELESS_STATUS = cfgROOMNUM)
            SEND_LEVEL vdvCOMM,4,3
        SEND_COMMAND vdvTP,'PAGE-Logo'
        SEND_COMMAND vdvTP,'PPON-Shutdown'
        WAIT_UNTIL (nPROJECTOR1_POWER = 0)
    	nCONFIG_MODE = 0
    	SEND_COMMAND vdvTP,'PPOF-Shutdown'
    (*                STARTUP CODE GOES BELOW                  *)
    (*                THE EVENTS GO BELOW                      *)
    BUTTON_EVENT[vdvTP,21]                           // VTC RESERVE
    	IF (VTC_STATUS=cfgROOMNUM)             	// IF ALREADY SELECTED, DESELECT
    	    SEND_STRING dvMixer,"'#70 MACRO 2',13"    // DISABLE 430 VTC
    	ELSE
    	    IF (VTC_STATUS=3)                 // IF AVAILABLE, SELECT
    	    SEND_STRING dvMixer,"'#70 MACRO 1',13"    // DISABLE 430 VTC
    		SEND_LEVEL vdvCOMM,1,cfgROOMNUM
        RELEASE:
    BUTTON_EVENT[vdvTP,22]                           // DVD RESERVE
    	IF (DVD_STATUS=cfgROOMNUM)             // IF ALREADY SELECTED, DESELECT
    	ELSE
    	    IF (DVD_STATUS=3)                 // IF AVAILABLE, SELECT
    		SEND_LEVEL vdvCOMM,2,cfgROOMNUM
        RELEASE:
    BUTTON_EVENT[vdvTP,23]                           // VCR RESERVE
    	IF (VCR_STATUS=cfgROOMNUM)            // IF ALREADY SELECTED, DESELECT
    	ELSE
    	    IF (VCR_STATUS=3)                 // IF AVAILABLE, SELECT
    		SEND_LEVEL vdvCOMM,3,cfgROOMNUM
        RELEASE:
    BUTTON_EVENT[vdvTP,24]                           // WIRELESS RESERVE
    	IF (WIRELESS_STATUS=cfgROOMNUM)   	// IF ALREADY SELECTED, DESELECT
    	    SEND_STRING dvMixer,"'#70 MACRO 4',13"    // DISABLE 430 WIRELESS
    	ELSE
    	    IF (WIRELESS_STATUS=3)             // IF AVAILABLE, SELECT
    		SEND_LEVEL vdvCOMM,4,cfgROOMNUM
    		SEND_STRING dvMixer,"'#70 MACRO 3',13"    // ENABLE 430 WIRELESS
        RELEASE:
    BUTTON_EVENT[vdvTP,28]                           // INDIVIDUAL MODE SELECTED
        RELEASE:
    	nCONFIG_MODE = 0
    	MIC_MODE = 0
    	AUDIO_INDIVIDUAL_MODE()
    	OFF[vdvTP,8]                             // MICS UNMUTED
    BUTTON_EVENT[vdvTP,29]                           // Combined MODE with Room B SELECTED
        RELEASE:
    	MIC_MODE = 0
    	IF (nB_STATUS)			// Room B IN USE
    	    SEND_COMMAND vdvTP,'PPON-Room B Busy'
    	    WAIT 100
    		SEND_COMMAND vdvTP,'@PPX'
    		SEND_COMMAND vdvTP,'PAGE-[Room Setup]Mode 3'
    	ELSE
    	    nCONFIG_MODE = 1
    	    SEND_COMMAND vdvTP,'PAGE-Main Page'
    	    SEND_COMMAND vdvTP,'PPON-[Nav 7]Nav 7'
    	    ON[vdvCOMM,1]
    	    AUDIO_COMBINED_AB_MODE ()
    BUTTON_EVENT[vdvTP,30]                           // Combined MODE with Both SELECTED
        RELEASE:
    	MIC_MODE = 0
    	    WAIT 100
    	ELSE
    	    IF (nC_STATUS)			// Room C IN USE
    		SEND_COMMAND vdvTP,'PPON-Room C Busy'
    		WAIT 100
    	    ELSE
    		nCONFIG_MODE = 2
    		ON[vdvCOMM,1]
    		ON[vdvCOMM,2]
    		AUDIO_COMBINED_ABC_MODE()
    BUTTON_EVENT[vdvTP,41]                           // DVD SELECTED
            ON[vdvTP,41]
        RELEASE:
    	IF (DVD_STATUS = 3)
    	    DO_PUSH (vdvTP,22)
    	IF (DVD_STATUS = cfgROOMNUM OR DVD_STATUS = 3)
    	  SEND_COMMAND vdvTP,'@PPX'      // CLEAR POPUPS
    	  SEND_COMMAND vdvTP,'PAGE-[DVR]DVR'
    	  SWITCH (nCONFIG_MODE)
    	    CASE 0:				// INDIVIDUAL MODE
    		AVSWITCH2_TIE (1,3)
    		IF (nPROJECTOR1_INPUT <> 8)
    		    nPROJECTOR1_INPUT = 8
    		    SET_PROJECTOR1_INPUT(nPROJECTOR1_INPUT)
    	    CASE 1:				// COMBINED WITH B
    		AVSWITCH2_TIE (1,3)
    		AVSWITCH2_TIE (1,2)
    		IF (nPROJECTOR2_INPUT <> 8)
    		    nPROJECTOR2_INPUT = 8
    		    SET_PROJECTOR2_INPUT(nPROJECTOR2_INPUT)
    	    CASE 2:				// COMBINED WITH B AND C
    		AVSWITCH2_TIE (1,3)
    		AVSWITCH2_TIE (1,2)
    		AVSWITCH2_TIE (1,1)
    		IF (nPROJECTOR3_INPUT <> 8)
    		    nPROJECTOR3_INPUT = 8
    		    SET_PROJECTOR3_INPUT(nPROJECTOR3_INPUT)
    LEVEL_EVENT[vdvCOMM,1]			// STATUS OF VTC
        VTC_STATUS = LEVEL.VALUE
        IF (VTC_STATUS = cfgROOMNUM OR VTC_STATUS = 3)
    	SEND_COMMAND vdvTP,'^ICO-2,1&2,0'   // NO ICON, DEVICE IS AVAILABLE
        ELSE
    	SEND_COMMAND vdvTP,'^ICO-2,1&2,1'   // NOT ICON, DEVICE IS not AVAILABLE
    LEVEL_EVENT[vdvCOMM,2]			// STATUS OF DVD
        DVD_STATUS = LEVEL.VALUE
    	SEND_COMMAND vdvTP,'^ICO-41,1&2,0'   // NO ICON, DEVICE IS AVAILABLE
        ELSE
    	SEND_COMMAND vdvTP,'^ICO-41,1&2,1'   // NOT ICON, DEVICE IS not AVAILABLE
    LEVEL_EVENT[vdvCOMM,3]			// STATUS OF VCR
        VCR_STATUS = LEVEL.VALUE
        IF (VCR_STATUS = cfgROOMNUM OR VCR_STATUS = 3)
    	SEND_COMMAND vdvTP,'^ICO-42,1&2,0'   // NO ICON, DEVICE IS AVAILABLE
        ELSE
    	SEND_COMMAND vdvTP,'^ICO-42,1&2,1'   // NOT ICON, DEVICE IS not AVAILABLE
    LEVEL_EVENT[vdvCOMM,4]			// STATUS OF WIRELESS
        WIRELESS_STATUS = LEVEL.VALUE
        IF (WIRELESS_STATUS = cfgROOMNUM OR WIRELESS_STATUS = 3)
    	SEND_STRING dvMixer,"'#70 MACRO 3',13"  //ENABLE WIRELESS IN 430
        ELSE
    	SEND_STRING dvMixer,"'#70 MACRO 4',13"  //DISABLE WIRELESS IN 430
    CHANNEL_EVENT[vdvCOMM,11]               // ROOM B STATUS
      ON:
    	nB_STATUS = 1		// ROOM IS BUSY
      OFF:
    	nB_STATUS = 0		// IN AVAILABLE MODE
    CHANNEL_EVENT[vdvCOMM,12]               // ROOM C STATUS
      ON:
    	nC_STATUS = 1		// ROOM IS BUSY
      OFF:
    	nC_STATUS = 0		// IN AVAILABLE MODE
    (*            THE ACTUAL PROGRAM GOES BELOW                *)
    DEFINE_PROGRAM
    (*                     END OF PROGRAM                      *)
    (*        DO NOT PUT ANY CODE BELOW THIS COMMENT           *)
    thanks guys
    Danny, thanks for the example, much clear how to do it now.
    What generate the channel event?
    I searched anywhere for info on levels and channel, and there very basic informaion on this topics...
  • In this case, the master in one of the other rooms will generate the channel event. For example, when a user touches the logo screen on the touch panel in room B, that master will issue the ON[vdvCOMM,11] statement. This lets the program running for room A know that it is not possible to go into combined mode with room B. When they touch the button to inititate the shutdown process for room B, the OFF[vdvCOMM,11] is issued.
    It works just like normal channel events. Any of the masters in the system with the virtual device defined can make changes to channels and levels.