Check to see if TP is online
At the moment I have a variable that changes itself to 1/0 on the online and offline data events from the TP. Is there a way to eliminate the need for this and do something like "if (dvTP = online)"?
  • jazzwyldjazzwyld Posts: 199
    Waiting to be trumped
    If you are truly trying to set something to change on ONLINE or OFFLINE Events, then that's where you should place your variable.
  • dchristodchristo Posts: 177
    I agree with Jeff, however, you can do this:
    if(Device_ID(dvTp) > 0)
    --D
  • jcereckejcerecke Posts: 40
    jazzwyld wrote: »
    My reasoning is this:
    I have a bargraph (or 6) on my TP which controls channels on an audio mixing desk via RS232. When the TP goes offline, it somehow generates a level event of 0 for all bargraphs, which then gets rid of all my audio.
    So I want to check if the TP is online when the level event occurs and if it is to change the level else do nothing.
  • kbeattyAMXkbeattyAMX Posts: 358
    jcerecke wrote: »
    What about just doing if (level.value) then control my mixing desk. However I would use a virtualTP for level control because it does not go off line. Combine the VirtTP with the RealTP.
    jcerecke wrote: »
    That is just an issue. When a panel goes offline it sends a level.event 0.
    Thats cool. Thanks for all the suggestions.
  • AuserAuser Posts: 506
    jazzwyld wrote: »
    No actually, kbeattyAMX is correct. If you combine the physical device(s) level with a virtual device level you WON'T get the level event with value = 0 when the/a physical device goes offline. This is because the virtual device never goes offline and therefore the level is always tracked in memory.
    It's possible to combine the levels using COMBINE_LEVELS or COMBINE_DEVICES. Using device arrays is generally better practice/more desirable than combining devices - as such COMBINE_LEVELS would be recommended.
    I'm not sure of the context in which you're dealing with the incoming level events, but something along these lines would achieve what you're after:
    // Physical devices
    dvTP_1                     = 10001:1:0
    dvTP_2                     = 10001:2:0
    dvTP_3                     = 10001:3:0
    vdvTP                      = 33001:1:0
    // Virtual which maintains the level regardless
    // of the online state of the physical devices
    vdvAUDIO                   = 33002:1:0
    DEFINE_CONSTANT
    // Index of the level being tracked
    char    LVL_VOLUME         = 1
    // A level on a virtual device is used to keep a
    // constant record of the level's current value
    devlev  lvlTRACKED_VOLUME  = {vdvAUDIO, LVL_VOLUME}
    // This is the level array to catch incoming level
    // events from (ie. from the panels)
    devlev  lvlTP_VOLUME[] =
      {vdvTP,  LVL_VOLUME},
      {dvTP_1, LVL_VOLUME},
      {dvTP_2, LVL_VOLUME},
      {dvTP_3, LVL_VOLUME}
    // Combine levels to prevent unwanted events
    // when physical devices go online/offline
    combine_levels(lvlTRACKED_VOLUME, lvlTP_VOLUME)
    level_event[lvlTP_VOLUME]
      // Handle the event here...
    The same can be achieved for devices which generate channel events when they go offline using COMBINE_CHANNELS.