Ademco Vista-128BPT

I just got an Ademco (Honeywell) Vista-128BPT (Turbo Series) for testing and tweaking the UI module before deploying it to the field and I noticed some flaws on the AMX documented feedback. Under the SECSTATUS-<status> there are 4 documented status:
ARMED
ARMED HOME
DISARMED
ALARM

The first 3 status work, but the ALARM one, which is extremely important doesn't. I armed the system to AWAY mode or fully armed and when I breach a zone, the alarm goes off but the AMX Comm module never sends out the ALARM or ALARMED status out. I've tried many times breaching different zones and still the same issue. Therefore, the feedback on touch panels never gets to show ALARM or ALARMED, it still has the ARM AWAY button lit, even though the alarm is going off.

Another issue is that I noticed is that the Zone Status is not reported correctly in the module when the system is armed to either AWAY or HOME. It does report correctly when the system is disarmed. Again, when the system is armed and a zone is breached, the alarm goes off, but the AMX module is not sending/processing the ALARM status, neither it is reporting which zone was breached. The way it is now, the module is not reliable. It basically provides arming and disarming, but the ALARM feedback and zone Status feedback is not reliable, especially when the system is alarming, when it should matter the most. The physical alarm keypad reports the breaches correctly.

Is there anything am missing here? The system is communicating correctly, but I am having these feedback issues. Have any of you noticed this limitation?

Thanks,

Ricardo

* Note: For those that want some type of individual zone feedback other than the simple text box, here is a function I edited from another alarm module to process it:
DEFINE_FUNCTION ProcessZones(CHAR sZnStr[])
{
    //SECPOINTSTATUS-90,ACTIVE
    //SECPOINTSTATUS-25,BYPASSED
    //SECPOINTSTATUS-15,FAULT
    //SECPOINTSTATUS-250,INVALID

    nConcZone = ATOI(REMOVE_STRING(sZnStr, ',', 1))
    
    SELECT
    {
        //  Send Fault bitmap
        ACTIVE(FIND_STRING(sZnStr , 'FAULT', 1) || 
               //FIND_STRING(sZnStr , 'INVALID', 1) ||
	       FIND_STRING(sZnStr , 'BYPASSED', 1)):
        {     
            ON[dvTP, dcZONE_ARRAY[nConcZone]]
	    dcZONE_STATUS[nConcZone] = 1
        }
        //  Send Secure bitmap
        ACTIVE(FIND_STRING(sZnStr , 'ACTIVE', 1)):  
        {
            OFF[dvTP, dcZONE_ARRAY[nConcZone]]
	    dcZONE_STATUS[nConcZone] = 0	    
        }        
    }    
}

Comments

  • a_riot42a_riot42 Posts: 1,624
    A bug in a Duet module? No...

    That's disappointing. I have a job in a couple weeks using that module so I can let you know what I find out. Security commands documents tend to be difficult or impossible to get, so this is not good to hear. Can you use the PASSBACK command to listen for the alarm command?
    Paul
  • ericmedleyericmedley Posts: 4,177
    I still use the older Netlinx module. I don't seem to recall it being an issue there. But before you all come clamoring for this version it does not support plain ole' number keypad button pushes.
  • Yes. This Duet version is very limited. There is a big disconnect between the arm buttons and the keypad emulation. To arm the system the UI is using the built-in TP keypad and since the emulated keypad has no text feedback, you can't see what the system is doing when using the module emulated keypad numbers and keys.

    ericmedley,

    Is it possible for you to upload the old non-duet module for us. It is not available from AMX anymore. Maybe it works better... as most non-duet modules do.

    Thanks,

    Ricardo
  • Never mind. The old module uses 1200 baud rate and the Vista-128BPT panel requires 9600 baud rate. I actually found an old version of the non-duet module, but there is no way to change the baud rate to 9600. It is by default inside the Comm module 1200 and we don't have the .axs file for the Comm module, only the .tko.
  • ericmedleyericmedley Posts: 4,177
    1200 baud is correct.

    But, at any rate, here it is folks.

    I wonder if you could just slam the rs232 port with baud 9600 commands. hmmmm... if it wasn't an alarm system it might be worth trying.
  • John NagyJohn Nagy Posts: 1,742
    Note that there are significant differences in talking to a 128BP/BPE and the newer BPT. Support at Honeywell will tell you they are the same. This is an outright lie.

    They also will NOT divulge the protocols. When we dug in hard, they admitted they were different and only disclosed to trusted corporate partners. AMX is forbidden to give out the protocol to dealers, only to provide the "black box" module. Which is woefully inadequate and faulty.

    They explain that this is to protect Honeywell from Chinese knock-off boards using a public protocol.

    So unless you backward engineer it like the Chinese are doing anyway*, you aren't going to get the BPT to be satisfying.

    (* - as we did... but can't share or we'll be sued)
  • ericmedleyericmedley Posts: 4,177
    I really miss the Destiny. I was genuinely angry when the discontinued it.
  • a_riot42a_riot42 Posts: 1,624
    Never mind. The old module uses 1200 baud rate and the Vista-128BPT panel requires 9600 baud rate. I actually found an old version of the non-duet module, but there is no way to change the baud rate to 9600. It is by default inside the Comm module 1200 and we don't have the .axs file for the Comm module, only the .tko.

    Did you call TS? If you complain they might pass it to the Duet group and someone might fix it.
    Paul
  • Yes. I did report it to tech support. There is another issue though in the UI module. The Arm, Arm Home and Disarm buttons rely on the built-in touch panel/iPad keypad to work, which is by default PORT 1. In my case, I can't use PORT 1 for the alarm, it is already used for IR devices. Usually I assign PORT 7 in my UI for alarm/security systems. In my case, the default UI won't work as I can't use PORT 1. Now, I have to redesign the UI to accept strings from PORT 7 instead of PORT 1, the default. My touch panel addresses are 10001:7:0, 10002:7:0, etc. I am sick of these duet modules that don't give us the tools to implement the module in the real World projects. In the past few years, I've found myself spending a lot of time trying to troubleshoot and rewrite Duet UI modules. The problem is that since we don't have access to the Comm modules (Black Boxes), we get really frustrated with Comm mudules that are not also doing what the support module documentation tells us that it should do. I miss the non-duet module days, where modules where better written and easier to implement.

    I haven't done a virtual keypad in years. Does anybody have a code sample for this? I basically need numbers 1 to 9 and the OK button to process it. In addition, a text box to append the digits entered, so the end user can see what he is typing. The idea is that after typing the password and pressing OK or Done, the string gets sent to the UI module out of PORT 7.

    Thanks,

    Ricardo
  • shr00m-dewshr00m-dew Posts: 394
    I know this works well with C4, Their protocol is available upon request.

    http://houselogix.com/products/hsim-security-adapter.asp

    Kevin D.
  • I found a workaround for the virtual keypad. All my button channels are on PORT 7, but the text inputs are on PORT 1. I am basically passing both 10007 and 10001 to the UI module. PORT 7 handles everything: events and feedback. PORT 1 just the text input. It works fine, but we still have the issue with the Comm Module not reporting the Alarm state, nor the zones feedback when the system is alarming. I am trying to see if AMX can help... See my modified UI module code below. I've changed the channel mapping to fit other function, as well as added a text box and individual zone feedback. On the TP4 file I created my own keypad.
    DEFINE_MODULE 'Ademco_Vista_Comm_dr1_0_0' DuetCode(vdvPRTN1, dvDevice)
    DEFINE_MODULE 'Ademco_Vista_UI'   TP1(vdvPRTNS, dvTP_Alarm1, nCHAN_BTNS, dcZONE_ARRAY, dviPad_Family)
    // dvTP_Alarm1 = 10007 & dviPad_Family = 10001
    
    MODULE_NAME='Ademco_Vista_UI' (DEV vdvPRTNS[], DEV dvTP, INTEGER nCHAN_BTN[], INTEGER dcZONE_ARRAY[], DEV dvTPText)
    (*{{PS_SOURCE_INFO(PROGRAM STATS)                          *)
    (***********************************************************)
    (*  FILE CREATED ON: 03/10/2005  AT: 13:15:35              *)
    (***********************************************************)
    (*  FILE_LAST_MODIFIED_ON: 05/26/2005  AT: 12:54:04        *)
    (***********************************************************)
    (*  ORPHAN_FILE_PLATFORM: 1                                *)
    (***********************************************************)
    (*!!FILE REVISION: Rev 0                                   *)
    (*  REVISION DATE: 04/27/2005                              *)
    (*                                                         *)
    (*  COMMENTS:                                              *)
    (*                                                         *)
    (***********************************************************)
    (*}}PS_SOURCE_INFO                                         *)
    (***********************************************************)
    
    (***********************************************************)
    
    (***********************************************************)
    (* REV HISTORY:                                            *)
    (***********************************************************)
    (*
        The Ademco BP and FBP systems use different mother boards and have
        different firmware. The BP systems use a simple protocol, while the
        FBP may be programmed to use the extended or simple protocols. See
        Main.axs notes for more information.
    
      The 128/250BP systems use a Simple protocol; the 128/250FBP systems
      can use a SImple or Extended protocol set. Use the FBP 1*78 and 1*79
      program steps to turn on Extended protocol and select Extended event
      messages. Use the PROPERTY command to tell the Comm module whether or
      not to use the Extended protocol set (See the Main.axs ONLINE event)
      
      This sample UI code is written to request and send the 4-digit password
      for the FBP systems, and the 2-digit user id followed by the 4-digit
      password, for the BP systems. This is because the NetLinx programmer will
      not know the user id number if new passwords are addded after install.
      The first user id is 2, and the default password is 1234. After this,
      user id 3, 4, etc. may be programmed for other passwords. The partition(s)
      controlled by any given password are determined by Vista system programming.
    *)
    
    (***********************************************************)
    (*          DEVICE NUMBER DEFINITIONS GO BELOW             *)
    (***********************************************************)
    DEFINE_DEVICE
    (***********************************************************)
    (*               CONSTANT DEFINITIONS GO BELOW             *)
    (***********************************************************)
    DEFINE_CONSTANT
    
    //Added by Ricardo 4/23/2014
    INTEGER nMAX_Zones               =   75	     // Define the Max number of zones used here
    
    #INCLUDE 'SNAPI.AXI'
        
    (***********************************************************)
    (*              DATA TYPE DEFINITIONS GO BELOW             *)
    (***********************************************************)
    DEFINE_TYPE
    (***********************************************************)
    (*               VARIABLE DEFINITIONS GO BELOW             *)
    (***********************************************************)
    DEFINE_VARIABLE
    
    VOLATILE CHAR sVERSION[5] = ''   // STORES NETLINX COMM MODULE VERSION NUMBER
    VOLATILE INTEGER nDEBUG = 0      // TRACKS THE ON/OFF STATE OF DEBUG MSGS SENT TO THE TELNET SESSION
    VOLATILE CHAR cARMTYPE[20]
    VOLATILE CHAR USER_NUMBER[] = '00' //DEFAULT USER NUMBER
    VOLATILE INTEGER nCURRENT_PRTN = 1	// Selected partition
    VOLATILE CHAR cPARTITION_STATUS[9][20]	// Status of all partitions - #9 (ALL) updated by fnDO_FEEDBACK
    VOLATILE CHAR cPOINT_STATUS[128]		// 128 or 250 zones supported
    VOLATILE CHAR cUSER_CODE[] = '1234'	// password to use for zone bypass (see function ToggleBypass)
    
    //Added by Ricardo 4/23/2014
    VOLATILE INTEGER nConcZone       =   0   //  Zone selection
    VOLATILE INTEGER dcZONE_STATUS[nMAX_Zones]		// 128 or 250 zones supported
    (***********************************************************)
    (*               LATCHING DEFINITIONS GO BELOW             *)
    (***********************************************************)
    DEFINE_LATCHING
    (***********************************************************)
    (*       MUTUALLY EXCLUSIVE DEFINITIONS GO BELOW           *)
    (***********************************************************)
    DEFINE_MUTUALLY_EXCLUSIVE
    (***********************************************************)
    (*        SUBROUTINE/FUNCTION DEFINITIONS GO BELOW         *)
    (***********************************************************)
    DEFINE_FUNCTION fnDO_FEEDBACK()
    {
        STACK_VAR INTEGER nINDEX
        // Highlight current partition, and check to see if all partitions same status
        cPARTITION_STATUS[9] = cPARTITION_STATUS[1]  // load with first status
        FOR (nINDEX = 1; nINDEX <= 9; nINDEX++)
        {
    	[dvTP, nCHAN_BTN[nINDEX + 15]] = (nCURRENT_PRTN == nINDEX)
    	IF(cPARTITION_STATUS[9] <> cPARTITION_STATUS[nINDEX])
    	    cPARTITION_STATUS[9]  = ''		// Clear #9 if no match
        }
        [dvTP, nCHAN_BTN[1]] = (cPARTITION_STATUS[nCURRENT_PRTN] == 'ARMED HOME' ||
    			    cPARTITION_STATUS[nCURRENT_PRTN] == 'ARMED_HOME')
        //[dvTP, nCHAN_BTN[2]] = (cPARTITION_STATUS[nCURRENT_PRTN] == 'ARM HOME NOW' ||
    	//		    cPARTITION_STATUS[nCURRENT_PRTN] == 'ARM_HOME_NOW')
        [dvTP, nCHAN_BTN[3]] = (cPARTITION_STATUS[nCURRENT_PRTN] == 'ARMED')
        [dvTP, nCHAN_BTN[4]] = (cPARTITION_STATUS[nCURRENT_PRTN] == 'DISARMED')
        [dvTP, nCHAN_BTN[25]] = (cPARTITION_STATUS[nCURRENT_PRTN] == 'ALARM')
        SWITCH(cPARTITION_STATUS[nCURRENT_PRTN])
        {
    	CASE 'ARMED_HOME':
    	CASE 'ARMED HOME':
    	{
    	    SEND_COMMAND dvTP,"'^TXT-1',',0,','ARMED TO HOME'"
    	}
    	CASE 'ARMED':
    	{
    	    SEND_COMMAND dvTP,"'^TXT-1',',0,','ARMED TO AWAY'"
    	}
    	CASE 'DISARMED':
    	{
    	    SEND_COMMAND dvTP,"'^TXT-1',',0,','DISARMED'"
    	}
    	CASE 'ALARM':
    	{
    	    SEND_COMMAND dvTP,"'^TXT-1',',0,','ALARMED'"
    	}
        }
    }
    
    DEFINE_FUNCTION ToggleBypass(INTEGER nZoneNumber)
    {
        STACK_VAR CHAR cString[6]
        
        cString = cUSER_CODE
        
        WHILE(LENGTH_STRING(cString))
        {
    	SEND_COMMAND vdvPRTNS[nCURRENT_PRTN],"'KEYPAD-',GET_BUFFER_CHAR(cString)"
        }
        
        SEND_COMMAND vdvPRTNS[nCURRENT_PRTN],"'KEYPAD-6'"
        
        cString = RIGHT_STRING("'00',ITOA(nZoneNumber)",3)
        WHILE(LENGTH_STRING(cString))
        {
    	SEND_COMMAND vdvPRTNS[nCURRENT_PRTN],"'KEYPAD-',GET_BUFFER_CHAR(cString)"
        }
    }
    
    //Added by Ricardo 4/23/2014/////////////////////////////////////////////////
    DEFINE_FUNCTION ProcessZones(CHAR sZnStr[])
    {
        //SECPOINTSTATUS-90,ACTIVE
        //SECPOINTSTATUS-25,BYPASSED
        //SECPOINTSTATUS-15,FAULT
        //SECPOINTSTATUS-250,INVALID
    
        nConcZone = ATOI(REMOVE_STRING(sZnStr, ',', 1))
        
        SELECT
        {
            //  Send Fault bitmap
            ACTIVE(FIND_STRING(sZnStr , 'FAULT', 1) || 
                   //FIND_STRING(sZnStr , 'INVALID', 1) ||
    	       FIND_STRING(sZnStr , 'BYPASSED', 1)):
            {     
                ON[dvTP, dcZONE_ARRAY[nConcZone]]
    	    dcZONE_STATUS[nConcZone] = 1
            }
            //  Send Secure bitmap
            ACTIVE(FIND_STRING(sZnStr , 'ACTIVE', 1)):  
            {
                OFF[dvTP, dcZONE_ARRAY[nConcZone]]
    	    dcZONE_STATUS[nConcZone] = 0	    
            }        
        }    
    }
    (***********************************************************)
    (*                STARTUP CODE GOES BELOW                  *)
    (***********************************************************)
    DEFINE_START
    
    fnDO_FEEDBACK()	// UPDATE PANEL AT START
    
    (***********************************************************)
    (*                THE EVENTS GOES BELOW                    *)
    (***********************************************************)
    DEFINE_EVENT
    
    
    DATA_EVENT[vdvPRTNS]
    {
    	COMMAND:
    	{
    		STACK_VAR CHAR DATUM[30]
    		
    		IF(nDEBUG >= 3)
    		{
    			send_string 0, "'UI received from Comm: ',data.text"
    		}
    		DATUM  = remove_string(data.text, '-', 1)
            
    		SWITCH(DATUM)
    		{
    			// FIND MATCHING STRING AND PARSE REST OF MESSAGE. PROVIDE FEEDBACK TO THE 
    			// TOUCH PANEL.
    			CASE 'DEBUG-': 
    			{	nDEBUG = ATOI(DATA.TEXT) 
    				IF (nDebug >= 3) 
    					SEND_STRING 0, "'Debug messages are now on.'"
    				ELSE IF(nDEBUG < 3)
    					SEND_STRING 0, "'Debug messages are now off.'"
    			}
    			CASE 'SECSTATUS-':
    			{
    			    STACK_VAR INTEGER nPRTN
    			    
    			    nPRTN = DATA.DEVICE.PORT		// Which partition?
    			    cPARTITION_STATUS[nPRTN] = DATA.TEXT	// Save status
    			    fnDO_FEEDBACK()		// Update panel buttons
    			}
    			CASE 'SECPOINTSTATUS-':
    			{
    			    SEND_COMMAND dvTP,"'^TXT-',ITOA(nCHAN_BTN[28]),',0,',DATA.TEXT"
    			    ProcessZones(DATA.TEXT) //Added by Ricardo 4/23/2014
    			} 
    			CASE 'VERSION-': 
    			{
    				sVERSION = DATA.TEXT 
    			}
    		}// END SWITCH(datum)
    		
    	}// END COMMAND
    }// END DATA_EVENT[vdvPRTNS]
    
    
    DATA_EVENT[dvTPText]
    {
    	ONLINE: 	
    	{
    	}
    	STRING:
    	{
    	    STACK_VAR INTEGER nINDEX
    		IF (nDEBUG) 
    			SEND_STRING 0, "'FROM THE KEYPAD: ',DATA.TEXT" 
    			
    		IF(FIND_STRING(DATA.TEXT, 'KEYP-', 1) == 1)
    		{
    			REMOVE_STRING(DATA.TEXT, 'KEYP-', 1)
    			
    			IF(DATA.TEXT == 'ABORT')
    			{
    			    // DO NOTHING...
    			}
    			ELSE IF(LENGTH_STRING(DATA.TEXT) >= 0 && LENGTH_STRING(DATA.TEXT) <= 6)
    			{
    			    STACK_VAR CHAR PASS_WORD[6]
    			    // PASSWORD MUST HAVE 4 DIGITS FOR EXTENDED PROTOCOL,
    			    // 6 DIGITS (USER + PW) FOR SIMPLE PROTOCOL
    			    // SO, ZERO FILL TO SIX DIGITS
    			    IF (nCURRENT_PRTN <= 8)
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'SECSTATE-',cARMTYPE,',',RIGHT_STRING("'00',DATA.TEXT",6)"
    			    ELSE	// FOR PARTITION 9, DO ALL 8
    			    {
    				FOR (nINDEX = 1; nINDEX <= 8; nINDEX++)
    				{
    				    SEND_COMMAND vdvPRTNS[nINDEX], "'SECSTATE-',cARMTYPE,',',RIGHT_STRING("'00',DATA.TEXT",6)"
    				}
    			    }
    			}
    			// ELSE PROMPT FOR PROPER PASSWORD FORMAT HERE...
    		}
    	}
    }// END DATA_EVENT[dvTP]
    
    BUTTON_EVENT[dvTP, nCHAN_BTN]
    {
    	PUSH:
    	{
    		STACK_VAR INTEGER nBTN
    		
    		nBTN = GET_LAST(nCHAN_BTN)
    		SWITCH(nBTN)
    		{
    			CASE 1:		//ARM TO HOME
    			{
    				cARMTYPE = 'ARM_HOME'
    				//SEND_COMMAND dvTP, "'@PKP-;ENTER PASS TO ARM TO HOME'"
    				//SEND_COMMAND dvTP, "'@PPN-Alarm Keypad'"
    				SEND_COMMAND dvTP,"'^TXT-2',',0,','ARM TO HOME'"
    			}
    			CASE 2:		//ARM TO HOME NOW
    			{
    				cARMTYPE = 'ARM_HOME_NOW'
    				//SEND_COMMAND dvTP, "'@PKP-;ENTER PASS TO ARM TO HOME NOW'"
    				//SEND_COMMAND dvTP, "'@PPN-Alarm Keypad'"
    				SEND_COMMAND dvTP,"'^TXT-2',',0,','ARM TO HOME NOW'"
    			}			
    			CASE 3:		//ARM TO AWAY
    			{
    				cARMTYPE = 'ARM'
    				//SEND_COMMAND dvTP, "'@PKP-;ENTER PASS TO ARM TO AWAY'"
    				//SEND_COMMAND dvTP, "'@PPN-Alarm Keypad'"
    				SEND_COMMAND dvTP,"'^TXT-2',',0,','ARM TO AWAY'"
    			}
    			CASE 4:		//DISARM
    			{
    				cARMTYPE = 'DISARM'
    				//SEND_COMMAND dvTP, "'@PKP-;ENTER PASS TO DISARM'"
    				//SEND_COMMAND dvTP, "'@PPN-Alarm Keypad'"
    				SEND_COMMAND dvTP,"'^TXT-2',',0,','DISARM'"
    			}
    			CASE 10:	//KEY PAD 0
    			CASE 11:	//KEY PAD 1
    			CASE 12:	//KEY PAD 2
    			CASE 13:	//KEY PAD 3
    			CASE 14:	//KEY PAD 4
    			CASE 15:	//KEY PAD 5
    			CASE 16:	//KEY PAD 6
    			CASE 17:	//KEY PAD 7
    			CASE 18:	//KEY PAD 8
    			CASE 19:	//KEY PAD 9
    			{    
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-',ITOA(nBTN - 10)"
    			    }
    			}
    			CASE 20:	//KEY PAD *
    			{
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-A'"
    			    }
    			}
    			CASE 21:	//KEY PAD #
    			{
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-B'"
    			    }
    			}
    			CASE 22:	//MACRO C: Fire
    			{
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-C'"
    			    }
    			}
    			CASE 23:	//MACRO D: Silent
    			{
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-D'"
    			    }
    			}
    			CASE 24:	//MACRO E: Medical
    			{
    			    IF (nCURRENT_PRTN <= 8)
    			    {
    				SEND_COMMAND vdvPRTNS[nCURRENT_PRTN], "'KEYPAD-E'"
    			    }
    			}
    			CASE 31:	// ACTIVE PARTITION SELECT
    			CASE 32:
    			CASE 33:
    			CASE 34:
    			CASE 35:
    			CASE 36:
    			CASE 37:
    			CASE 38:
    			CASE 39:
    			{    
    			    nCURRENT_PRTN = nBTN - 30	// REMEMBER PARTITION
    			}
    		    }// END SWITCH(nBTN)
    		    
    		    fnDO_FEEDBACK()	// UPDATE PANEL
    	}// END PUSH
    }// END BUTTON_EVENT[dvTP, nCHAN_BTN]
    (***********************************************************)
    (*            THE ACTUAL PROGRAM GOES BELOW                *)
    (***********************************************************)
    DEFINE_PROGRAM
    
    [dvTP, nCHAN_BTN[26]] = [vdvPRTNS[1],251]	// ONLINE
    [dvTP, nCHAN_BTN[27]] = [vdvPRTNS[1],252]	// DATA INITIALIZED
    
    //Zone feedback
    WAIT 1
    {
        [dvTP, 101] = (dcZONE_STATUS[1] == 1)
        [dvTP, 102] = (dcZONE_STATUS[2] == 1)
        [dvTP, 103] = (dcZONE_STATUS[3] == 1)
        [dvTP, 104] = (dcZONE_STATUS[4] == 1)
        [dvTP, 105] = (dcZONE_STATUS[5] == 1)
        [dvTP, 106] = (dcZONE_STATUS[6] == 1)
        [dvTP, 107] = (dcZONE_STATUS[7] == 1)
        [dvTP, 108] = (dcZONE_STATUS[8] == 1)
        [dvTP, 110] = (dcZONE_STATUS[10] == 1)
        [dvTP, 112] = (dcZONE_STATUS[12] == 1)
        [dvTP, 113] = (dcZONE_STATUS[13] == 1)
        [dvTP, 114] = (dcZONE_STATUS[14] == 1)
        [dvTP, 118] = (dcZONE_STATUS[18] == 1)
        [dvTP, 119] = (dcZONE_STATUS[19] == 1)
        [dvTP, 120] = (dcZONE_STATUS[20] == 1)
        [dvTP, 121] = (dcZONE_STATUS[21] == 1)
        [dvTP, 122] = (dcZONE_STATUS[22] == 1)
        [dvTP, 123] = (dcZONE_STATUS[23] == 1)
        [dvTP, 124] = (dcZONE_STATUS[24] == 1)
        [dvTP, 125] = (dcZONE_STATUS[25] == 1)
        [dvTP, 126] = (dcZONE_STATUS[26] == 1)
        [dvTP, 127] = (dcZONE_STATUS[27] == 1)
        [dvTP, 128] = (dcZONE_STATUS[28] == 1)
        [dvTP, 129] = (dcZONE_STATUS[29] == 1)
        [dvTP, 130] = (dcZONE_STATUS[30] == 1)
        [dvTP, 131] = (dcZONE_STATUS[31] == 1)
        [dvTP, 132] = (dcZONE_STATUS[32] == 1)
        [dvTP, 134] = (dcZONE_STATUS[34] == 1)
        [dvTP, 135] = (dcZONE_STATUS[35] == 1)
        [dvTP, 136] = (dcZONE_STATUS[36] == 1)
        [dvTP, 137] = (dcZONE_STATUS[37] == 1)
        [dvTP, 138] = (dcZONE_STATUS[38] == 1)
        [dvTP, 139] = (dcZONE_STATUS[39] == 1)
        [dvTP, 140] = (dcZONE_STATUS[40] == 1)
        [dvTP, 141] = (dcZONE_STATUS[41] == 1)
        [dvTP, 158] = (dcZONE_STATUS[58] == 1)
        [dvTP, 159] = (dcZONE_STATUS[59] == 1)
        [dvTP, 160] = (dcZONE_STATUS[60] == 1)
        [dvTP, 161] = (dcZONE_STATUS[61] == 1)
        [dvTP, 162] = (dcZONE_STATUS[62] == 1)
        [dvTP, 163] = (dcZONE_STATUS[63] == 1)
        [dvTP, 165] = (dcZONE_STATUS[65] == 1)
        [dvTP, 166] = (dcZONE_STATUS[66] == 1)
        [dvTP, 167] = (dcZONE_STATUS[67] == 1)
        [dvTP, 168] = (dcZONE_STATUS[68] == 1)
        [dvTP, 169] = (dcZONE_STATUS[69] == 1)
        [dvTP, 170] = (dcZONE_STATUS[70] == 1)
        [dvTP, 171] = (dcZONE_STATUS[71] == 1)
        [dvTP, 172] = (dcZONE_STATUS[72] == 1)
        [dvTP, 173] = (dcZONE_STATUS[73] == 1)
        [dvTP, 174] = (dcZONE_STATUS[74] == 1)
        [dvTP, 175] = (dcZONE_STATUS[75] == 1)
    }
                                            
    (***********************************************************)
    (*                     END OF PROGRAM                      *)
    (*        DO NOT PUT ANY CODE BELOW THIS COMMENT           *)
    (***********************************************************)
    
  • I kept digging into the Ademco settings and talked to an alarm expert with experience configuring the Ademco VISTA-128BPT and after additional settings, the ALARM feedback and zone breach now works. Apparently, since the 128BPT has a built-in serial port, some of the data fields differ a little from other panels. Also there is a need to enter Alt programming to set some other fields. Here is the settings I did:

    To enter Programming: Installer Code + 8 + 0 + 0 + 0

    Program *05: Enter 1 to view all zone faults/restores, enter 0 to view only events enabled in 1*79
    Program *14: Enter 1 to set RS232 input at TB4 (Built-in Serial Port)
    Program *79: Zone types restore reports for types 1-8 set to 1
    Program *80: Zone types restore reports for types 9,10,16 and 14 set to 1

    SETTINGS these last 3 made the difference
    Program 1*78: Enter 1 for Extended Protocol Event reports, enter 0 for Simple
    Program 1*79: To enable Event Log Types, enter 1 for each entry, 0 = disable
    Program 1*80: When enabled automatically transfers zone fault/restore data of the RS232 output (TB4)

    To program a field like 1*78 you need to enter the ALT PROGRAMMING by using #94 while in regular programming mode, then just enter *78 as regular programming. This was what hold me up until talking to an alarm expert.

    Cheers!
  • a_riot42a_riot42 Posts: 1,624
    I assumed you had the security settings correct prior to programming. Sounds like the module should work just fine then, which is a relief to me, since I have to integrate one here in a week or two. Most security systems do require a substantial amount of config to work with automation systems, since they aren't typically configured by default to do so, since there are security issues involved. Glad to hear the module will work ok.
    Paul
  • ericmedleyericmedley Posts: 4,177
    Thanks for posting this useful info Ricardo! And I echo a_riot's gladness of the module working. Security integration always makes me a little itchy anyway and having a reliable comm module helps allay some of my fears.
  • trobertstroberts Posts: 228
    I gave up on the AMX module and installed a cheap Cres... processor from EBay with their Ademco module running and then I pass strings back and forth to AMX via the Cres... processor using my own "protocol" Although it sounds like a lot of hassle, it took me 2 days vs 4 days and still getting no where using AMX alone. The end result was better than anything I was able to do using only the AMX module.