"NOT IN CONTROL OF AXlink" error
[Deleted User]
Posts: 0
in AMX Hardware
I am new to AMX. I have 2 EL Touch screens and a Axcent3. My problem
is getting the Axcent3 to be in control of the AXlink. When I don't
have anything connected to the AXlink, the Axcent will do the following:
>HAVE PROGRAM
PROGRAM IS PRESENT
>HAVE CONTROL
HAS CONTROL OF AXlink
SO the Axcent is in control, great. As soon as I plug in a touch
panel, I get:
AXcess System Reset
AXCENT III/PRO Integrated v5.04
Copyright 1992-2001 AMX Corp.
>HAVE PROGRAM
PROGRAM IS PRESENT
>HAVE CONTROL
NOT IN CONTROL OF AXlink
The touch panel is set to the same device ID as specified in my
program, 128. Serial Master Mode is off (non iluminated). And it is
set to BUSS MODE. Yet it looks like the Touch Panel is stealing the
AXlink away. Why?
Show Device on the Touch Panel also says, no Master Response.
Any ideas?
Thanks.
is getting the Axcent3 to be in control of the AXlink. When I don't
have anything connected to the AXlink, the Axcent will do the following:
>HAVE PROGRAM
PROGRAM IS PRESENT
>HAVE CONTROL
HAS CONTROL OF AXlink
SO the Axcent is in control, great. As soon as I plug in a touch
panel, I get:
AXcess System Reset
AXCENT III/PRO Integrated v5.04
Copyright 1992-2001 AMX Corp.
>HAVE PROGRAM
PROGRAM IS PRESENT
>HAVE CONTROL
NOT IN CONTROL OF AXlink
The touch panel is set to the same device ID as specified in my
program, 128. Serial Master Mode is off (non iluminated). And it is
set to BUSS MODE. Yet it looks like the Touch Panel is stealing the
AXlink away. Why?
Show Device on the Touch Panel also says, no Master Response.
Any ideas?
Thanks.
0
Comments
Yikes... Sounds like you have some REALLY old firmware in that panel, like - early rev2 or even rev1. It could be one of those settings, a short or reversal in your Axlink wiring, (plugging in a touch panel shouldn't reset the Axcent3) or bad Axlink tranceiver chips in either the Axcent3, the panel, or both.
If you have access to any Axlink device besides a panel (AXB-VOL3? Anything?) I'd try plugging that in and seeing if the Axcent3 is still happy and in control of the bus or not.
- Chip
Power is adaquate, two 13.8v power supplies, one feeding the Ax3, the other powering one or both panels, the Ax3 and panels are hooked up with AXM, AXP and Ground wires.
Unfortunately we dont have any other bits to test the setup with other than two EL touch panels.
I've written a simple program to run on his Ax3 that monitors IO port 1 for an input change and sets relay1 to high when input 1 is shorted to ground, The Ax3 was sluggish at responding to this input with no panels connected
We're currently letting the Ax3 sit with no backup batteries to let it clear any original program, it seems to accept programs ok, but the AXlinkLED is doing some weird stuff, sometimes flashing once, twice, and 3 times, randomly, with no TP's connected :S
AXT-EL+ TiltScreen Touch Panel 1.5 Amps
I got this out to the AXPower.txt.
I know this sounds basic, but are the touch panels set to
different device numbers??
The earlier posts only indicated a device of 128.
When I power them on, the AXLink goes steady on and the Axcent3 reboots, Then it says Not in control of AXlink in the terminal.
When I turn the TP's off again it says Has control of AXLink in the terminal, but the LED begins the blinking tantrum again.
Do you think that a Axcent3 firmware upgrade would help? Maybe also for the TP's?
BTW, The Axcent 3 is v5.04 and the TP's are v2.50 and v2.51.
Link to the datasheet:
http://pdf.alldatasheet.com/datasheet-pdf/view/80657/SIPEX/SP485RCN/TR.html
At the end it turned out of a bad power supply. Measuring with a digital voltage meter say that everything was ok. Measuring the output with a scope told us that the dc wasn't dc but single fase. Later we see that a diode has broke down. So be sure you're power supply is ok. Have you tryed to changed them with an other?
Good luck
I am really sure this is not a power related issue now. Seeing as I got this Axcent3 off ebay I tried to see if the seller would consider a refund. No luck there. Oh well.
I have one last idea, perhaps that SP485RCN RS-485 Transceiver chip is fried. It is getting the proper 5V to it but the voltages tested across Gnd to AXM and Gnd to AXP differ from Electro's Axcent3. I have sent Sipex, the manufacturer of the chip, a request for a free sample. Hopefully they will send me some and I can try replacing the transciever chip. I can't seem to locate this chip at any online electronics components stores. :-/
Thanks for the help so far. If I can get a new chip I will definately let you all know in case someone in the future needs help in this weird situation.
For now I have been using the serial port on one of my TP's to send serial strings to one of the Axcent3's serial ports. This works fine but it's not the same as using the AXlink. :-)
I have noticed that when I send serial data to each of the 6 serial ports, the RX LED's blink only on ports 2, 3, 4, and 6. Ports 1 and 5 seem dead. BUT, maybe I have them set to an incorrect mode like 422 or 485? I have not messed with that yet.
If they're set for hardware handshaking (HSON) and you're using a cable with just TX, RX and Ground, the RX LEDs won't blink.
- Chip
I ordered a replacement chip for the RS485 transciever in the Axcent3 that is at the heart of the AXLink port. The part inside the Axcent3 that I suspected was bad is a SIPEX 485RCN. I ordered a ST485EBD from Mouser.com. It is the same chip, just made by a different company. The hard part was removing the old chip and putting in the new one because they are surface mount chips. I've soldiered surface mount before so it worked out ok.
I am happy to report that it now works! The touch panels now have the flashing AXlink button and I no longer get any error codes from the LED.
Thanks to everybody for all the great tips and support!
Here's some pictures.
http://ip.gliebetronics.com:800/axlink_fixed/axlink_fixed_01.jpg
http://ip.gliebetronics.com:800/axlink_fixed/axlink_fixed_02.jpg
http://ip.gliebetronics.com:800/axlink_fixed/axlink_fixed_03.jpg
-Dan