Daikin itouch controller

Hello,
Has anyone written a module or include for a Daikin iTouch Controller? I am able to read statuses but i'm having trouble making changes to the set points. I suspect i'm doing something incorrect with the Endian conversion.

This protocol is way overly complex for what it does. I'm really hoping someone else has had some luck on this.

Comments

  • ericmedleyericmedley Posts: 4,177
    perhaps post the protocol doc and some of your non-working code. Who knows.. maybe it's easy enough to just fix what you have.
  • sling100sling100 Posts: 123
    It's very convoluted and requires IEEE temperature encoding. You also need an old version of the web software as I don't think the new version will let you connect to it at all? You need to POST a command to port 80 with all of the required info. Document attached - an example is posted on page 12. Good luck ...!

    Simon
  • daveruvolodaveruvolo Posts: 8
    Thank you for your reply. I have that page from the protocol doc as well. Below is a snippet of code i'm using to see if i can successfully change the temperatire in zone 1. when i sent this i get the HTTP ok response but it doesn't actually make any changes. i'm sure at least one of the values I have below are incorrect causing it to not actually perform the command. You can ignore the $FF,$FF,$FF at the end. That is a delimiter i am using so when my timeline runs i know if i have a command to send out. it gets chopped off before actually going out.

    cSendData = "'POST /cmd HTTP/1.1',$0d,$0a,
    'Content-Length: 56',$0d,$0a,
    'Content-Type: application/octet-stream',$0d,$0a,$0d,$0a,
    $38,$00,$00,$00, //command size is 56
    $76,$11,$01,$00, //command id is 70006
    $01,$00,$00,$00, //number of AC to set status- zone 1
    $00,$00,$00,$00, //reserved 1
    $00,$00,$00,$00, //reserved 2
    $00,$00,$00,$00, //reserved 3
    $00,$00,$00,$00, //reserved 4
    $00,$00,$00,$00, //reserved 5
    $00,$00,$00,$00, //ac address (0 is try on 1, 1 is try on 2, 2 is try on 3)
    $03,$00,$00,$00, //setting bit enabled
    $01,$00, //on/off is set to on
    $04,$00, //operation mode set to cool
    $01,$00, //ventillation mode set to auto
    $01,$00, //ventillation amount set to auto
    $41,$BC,$00,$00, //this is the temp value 73
    $00, //fan speed
    $00, //fan direction
    $00, //filter sign reset
    $00" //reserved 6
    strDaikinTxBuffer = "strDaikinTxBuffer,cSendData,$FF,$FF,$FF"
  • sling100sling100 Posts: 123
    You have all of the mode bits back to front, so 'op mode cool' is $00,$04 not $04,$00. Power on is $00,$01 etc. I would also change the setting bit to $7F to enable all of them.

    See if that works!

    Simon
  • KrondorKrondor Posts: 14
    Why would you go for I tocuh? there are other Gateway devices, much easier to work with, and also have AMX drivers. No delays, no setup, much easier to work with...