MVP Panel falls Offline
in AMX Hardware
An install with a NI3100 and 2 MVP7500 panels, both panels run identical TP4 designs.
The client reported that the 2nd Panel drops offline repeatedly. This was verified on-site, with good wireless connection but no connection to the master, Panel otherwise ok. 1st panel is absolutely fine and has never dropped off once. Master OK and fully responsive.
Only method to restore connection to system for Panel 2 was with a reboot of the master. Reboot of Panel 2 makes no difference - if connected - reconnects ok, if offline - stays offline.
Swapped out the wireless AP and improvement noted - less dropouts. No IP conflicts, no other network devices. Panels are in a dividing room so not environmental differences.
Panel 2 has again started dropping offline again!!
Everything has latest firmware.
Any thoughts other than swapping the panel?
It's possible as well there is something in the code like a lot of traffic to the panels causing congestion. I have a job where the wired panels drop off and on sporadically; but they do this so quickly, you would never know except by reading the log.
It was on a newer AMX WAP250, swapped this to an older WAP200G which had been working fine on my desk for months and months.
I don't believe there is an environmental reason - the panels are in effect side by side, panel 1 has never dropped off, panel 2 does regularly and doesn;t come back on. TP file is identical and so is the code running both panels on the master...
Interesting... When I've had to upgrade the CF Wireless Cards to accept European Wireless Channels (ie upto 13), most cards accept this update and work fine, others error on the update but work fine on the US only channels (upto 11)...
I'll give it a try later in the week and see what happens!!!
1. Try shifting the WAP channel.
2. Definitely swap to another vendors WAP and monitor the behavior.
My two bobs worth
You might also want to set the master to 10/half instead of auto detecting
Thanks for all the suggestions. Having just got back from site, we have discovered the problem. Next door is... Nortel Networks test labs! Serious randomly occuring interference on broad spectrum both in 2.4GHz range and surrounding freqs... changes from minute to minute, obviously not operational during construction phase...
Solution was to put entire system on to Nortel supplied WLAN (which is designed to be protected!) quite why or how the customer knew / warned this would effect their IT WLAN but not the AV system is anyones guess... Thank god MVP's have proper encryption built in nowadays.
Lesson - Never, ever rule out the environmentals!!
