Axcent3 Pro Dial In Modem Problem
hcary
Posts: 1
in AMX Hardware
Hi-
We control an Axcent3 pro by dialing into a modem that has a serial connection into one of the rear slots (not to be comfused with RS232 port). We are one of 7 media groups that use this Axcent3)
We're using a no-name modem that works, but needs to be replaced. I brought in a US Robotics modem, similar to the modems other groups are using to control. Using the same dip settings, I can't get commands to go through to the controller.
Any idea why?
Thanks - Hank
We control an Axcent3 pro by dialing into a modem that has a serial connection into one of the rear slots (not to be comfused with RS232 port). We are one of 7 media groups that use this Axcent3)
We're using a no-name modem that works, but needs to be replaced. I brought in a US Robotics modem, similar to the modems other groups are using to control. Using the same dip settings, I can't get commands to go through to the controller.
Any idea why?
Thanks - Hank
0
Comments
You need to mod a whole bunch of registers using the AT command most likely to fix this issue.
&K0 // hardware flow control off (I think - can't remember!!)
&D0 //DTR off
&C0 // ignores the state of the carrier - VERY useful through PABX where carrier signalling can be suspect
S0=2 //auto answer after 2 rings
&W0 // store all data in profile 0
&Y0 // run profile 0 on startup
This is from memory - hope it helps