Hey all.

Trying to connect two masters and having some issues. I've done a number of other similar units just fine, but this one is causing issues.

Master 1 is an NI-3100, System 1. URL for Master 2 is on this NI.
Master 2 is an NI-900, System 2. No URLs defined.

The masters are on their own network and can see eachother fine, and connect. However, only device 0 on the remote master is visible to each NI. The NIs can talk to their own devices, but not to eachother - in code or via telnet.

Below is with no code running.
Master 1:
>show system /min

Local devices for system #1 (This System)
----------------------------------------------------------------------------
Device (ID)Model                 (ID)Mfg                    FWID  Version
00000  (00299)NI Master          (00001)AMX Corp.           00380 v3.30.371
05001  (00286)NI-3100            (00001)AMX Corp.           00383 v1.13.6
10001  (00323)MVP 8400           (00001)AMX Corp.           00592 v2.81.21

Local devices for system #2
----------------------------------------------------------------------------
Device (ID)Model                 (ID)Mfg                    FWID  Version
00000  (00285)NI Master          (00001)AMX Corp.           00296 v3.30.371
Master 2:
>show system /min

Local devices for system #1
----------------------------------------------------------------------------
Device (ID)Model                 (ID)Mfg                    FWID  Version
00000  (00299)NI Master          (00001)AMX Corp.           00380 v3.30.371

Local devices for system #2 (This System)
----------------------------------------------------------------------------
Device (ID)Model                 (ID)Mfg                    FWID  Version
00000  (00312)NI Master          (00001)AMX Corp.           00341 v3.30.371
05001  (00286)NI-900             (00001)AMX Corp.           00382 v1.12.140
AMX tech support basically told me that it is a "known bug" with no possible workaround. I have recently installed a number of these systems using an NI-3100/NI-900 combination without a problem though... what gives? Any advice?

EDIT: Tried an NI-3000 in place of the NI-900, and it does the same thing. I'm thinking it is some setting or bug with the NI-3100, but don't know what it could be...

Comments

  • a_riot42a_riot42 Posts: 1,624
    true wrote:
    Hey all.

    Trying to connect two masters and having some issues. I've done a number of other similar units just fine, but this one is causing issues.

    Master 1 is an NI-3100, System 1. URL for Master 2 is on this NI.
    Master 2 is an NI-900, System 2. No URLs defined.

    The masters are on their own network and can see eachother fine, and connect. However, only device 0 on the remote master is visible to each NI. The NIs can talk to their own devices, but not to eachother - in code or via telnet.

    Below is with no code running.
    Master 1:
    >show system /min
    
    Local devices for system #1 (This System)
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version
    00000  (00299)NI Master          (00001)AMX Corp.           00380 v3.30.371
    05001  (00286)NI-3100            (00001)AMX Corp.           00383 v1.13.6
    10001  (00323)MVP 8400           (00001)AMX Corp.           00592 v2.81.21
    
    Local devices for system #2
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version
    00000  (00285)NI Master          (00001)AMX Corp.           00296 v3.30.371
    
    Master 2:
    >show system /min
    
    Local devices for system #1
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version
    00000  (00299)NI Master          (00001)AMX Corp.           00380 v3.30.371
    
    Local devices for system #2 (This System)
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version
    00000  (00312)NI Master          (00001)AMX Corp.           00341 v3.30.371
    05001  (00286)NI-900             (00001)AMX Corp.           00382 v1.12.140
    
    AMX tech support basically told me that it is a "known bug" with no possible workaround. I have recently installed a number of these systems using an NI-3100/NI-900 combination without a problem though... what gives? Any advice?

    EDIT: Tried an NI-3000 in place of the NI-900, and it does the same thing. I'm thinking it is some setting or bug with the NI-3100, but don't know what it could be...

    It sounds like a networking problem to me. What do you mean by the masters are on their own network? What are the IP configurations (IP/subnet mask/gateway) for each master? What do you mean by device 0?
    Paul
  • truetrue Posts: 307
    a_riot42 wrote:
    It sounds like a networking problem to me. What do you mean by the masters are on their own network?
    There are no PCs or other outside devices on this network - just the two NIs, a WAP and a touchpanel. And my notebook, of course, but only while testing / uploading code.
    a_riot42 wrote:
    What are the IP configurations (IP/subnet mask/gateway) for each master?
    10.0.110.0/24
    NI-3100 is .10
    NI-900 is .11
    WAP-250G is .240
    MVP-8400 is .51
    notebook is .250.

    Gateway, when unset, gave UDP errors; set to master NI (no communications are out of the subnet anyway). Wired connections are through unmanaged 5-port Linksys workgroup switch, which is how the NIs are. Just for giggles, with only the NIs hooked up directly to each other, the problem persists. IP settings are the same as what my other working units are using.
    a_riot42 wrote:
    What do you mean by device 0? Paul
    Exactly what I said - if you look at the system information in my post, each master can only see device 0 (NI Master) on the networked master. Specifically, they can't see device 5001 - that's all I need :)
  • a_riot42a_riot42 Posts: 1,624
    You didn't include your subnet mask and gateway numbers for the master.

    IIRC having nothing or incorrect data in the gateway field will cause problems although I don't know exactly what they are or why this happens. You may need to experiment with the gateway address, but making it the IP address of the other master I don't think will work. You should be able to leave them blank but I don't think the NIs like that so you many need to try a few things. You might try 127.0.0.1, or the APs IP address.
    Paul
  • truetrue Posts: 307
    a_riot42 wrote:
    You didn't include your subnet mask and gateway numbers for the master.
    I did. The netmask is /24, aka 255.255.255.0, or equivalent to Class C. I've also stated what I have the gateway set to - first unset (which on AMX gear is 0.0.0.0), then with the IP of the NI-3100 (which I specified above as 10.0.110.10). Since I am not communicating to / from the outside world, the gateway shouldn't matter (but AMX uses this to determine broadcast instead of ip/netmask, or so I've read, so it should be set if anything to not see UDP errors).

    The gateway is not used if you are communicating within the same subnet, so technically, it shouldn't matter.

    I don't see how this would break for these two specific NIs anyway, when it works fine for dozens of others.
    a_riot42 wrote:
    IIRC having nothing or incorrect data in the gateway field will cause problems although I don't know exactly what they are or why this happens.
    Exactly. As stated above, this should only cause problems with talking to the outside world, or with AMX's broadcast implementation. Since I'm not even dealing with broadcast traffic, it shouldn't make any difference.
    a_riot42 wrote:
    You may need to experiment with the gateway address, but making it the IP address of the other master I don't think will work. You should be able to leave them blank but I don't think the NIs like that so you many need to try a few things. You might try 127.0.0.1, or the APs IP address. Paul
    Yet again, it shouldn't matter, since I'm not talking to the outside world.

    With all that said, I hooked up the NI-3000 in the NI-3100's place and still have the same issue. I can play with the gateway all day and it makes no difference - same IP as NI, IP of other NI, IP of anything else, 127.0.0.1, 0.0.0.0 - doesn't matter. Even directly connected I have the issue. I can talk to both NIs fine over ethernet, and they do this with a direct cable connection, so I am rather stumped.
  • a_riot42a_riot42 Posts: 1,624
    true wrote:
    I did. The netmask is /24, aka 255.255.255.0, or equivalent to Class C.

    Fine, but I didn't know that you knew that so I was just asking to make sure.

    Why are you using an IP address in the Class A range but then a Class C subnet mask? Change you subnet masks to 255.0.0.0.
    Paul
  • truetrue Posts: 307
    Paul,

    Thanks to subnets, we can partition off pieces of networks as we wish - since 10.x.x.x is a class A _private_ network, we have that entire range, although via subnets, we can partition it as we wish. RFC1918 declares that we can do with these ranges as we wish.

    That being said, even with many individual successful installs at this complex using this subnet, I changed IPs on these NIs. No change to the system. I changed the subnet but kept the same IPs. No change to the system. This isn't an IP / networking problem. The systems can _see eachother_ fine, and can even _connect to eachother_, they just don't see any device other than device 0. I can have one ping the other all day.

    Right now, I have two NIs hooked up, running no code, via one 200ft tested patch cable and I am still experiencing this issue. I'm about to just defenestrate this equipment and get new gear.
  • a_riot42a_riot42 Posts: 1,624
    255.0.0.0 is the default subnet mask for all Class A addresses, 255.255.255.0 is the default subnet mask for all Class C addresses If you are subnetting then you would divide the address space up accordingly and use a different subnet mask. However, since you are not subnetting, then 255.0.0.0 is the correct subnet mask. Whether this fixes your problem or not I don't know, but at least then you can rule out network addressing/masking/gateway issues.
    true wrote:
    Right now, I have two NIs hooked up, running no code, via one 200ft tested patch cable and I am still experiencing this issue. I'm about to just defenestrate this equipment and get new gear.

    I have done many M2M installs and have never had any problems seeing the other masters devices. I will be very surprised if it ends up being a hardware/firmware issue.

    Paul
  • truetrue Posts: 307
    Paul,

    The point I was trying to make is that it is perfectly valid and legal to use the IPs I am using - whether they are public, private, or anything else, the equipment doesn't care - as long as the equipment is in the same specified subnet (which I am obviously using), it should work.

    (By using a broader subnet, other equipment in the 10.0.0.0/8 range could talk to my equipment, which I don't necessarily want. Subnets - more more appropriately, CIDR, which replaces Classes, are a solution. The numbers in the IP don't matter, as long as they are valid and won't cause conflicts - by using a range in 10.0.0.0/8, I know that if this network ever goes online, it won't have any conflicts. And, since 10.0.0.0/8 is a non-routable, local range, I can arrange any address in that range into as many subnets that I wish. You can do the same with 192.168.0.0/16 - in fact, many people do, as 192.168.1.0/24 or 192.168.0.0/24! For a reference, check http://en.wikipedia.org/wiki/Classless_Inter-Domain_Routing)

    I could use 1.1.1.1 and 1.1.1.2 in 255.255.255.252 and it'd still communicate as it is now (although not work as it should be, as it is now). And I did try other IPs, 192.168.1.1 and 192.168.1.2 on /24, and the problem still exists.

    This is _not_ a problem with the IP addressing. Give me examples and I'll set them and it still won't work. If there are any other commands, features, bugs, options, or whatever that could cause this to happen, it'd be helpful to know.
    a_riot42 wrote:
    I have done many M2M installs and have never had any problems seeing the other masters devices. I will be very surprised if it ends up being a hardware/firmware issue.
    I have as well, and this is the first time I've had this issue, which is why I am asking here. All of the other installs I have completed in this building - or elsewhere, for that matter - haven't had any issues.

    (PS - I've since moved the NI-900 to within 2ft of the NI-3100 with a factory 5ft crossover patch cable. The problem still exists.)

    EDIT: If it helps at all, here is a copy from the serial terminal of show system, with full verbosity:
    Local devices for system #1 (This System)
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version   
    00000  (00299)NI Master          (00001)AMX Corp.           00380 v3.30.371
           (PID=0:OID=0) Serial='210505x3470368',0,0    
           Physical Address=IP 10.0.110.10:1319 (00:60:9f:92:42:cc)
             (00299)vxWorks Image    (00001)                    00378 v3.30.371
             (PID=0:OID=1) Serial=N/A                     
             (00299)BootROM          (00001)                    00379 v3.30.371
             (PID=0:OID=2) Serial=N/A                     
             (00256)AXLink I/F uContr(00001)                    00270 v1.13.7
             (PID=0:OID=3) Serial=0000000000000000        
    05001  (00286)NI-3100            (00001)AMX Corp.           00383 v1.13.7
           (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0,
           Physical Address=Internal Connection
    
    Local devices for system #2 
    ----------------------------------------------------------------------------
    Device (ID)Model                 (ID)Mfg                    FWID  Version   
    00000  (00312)NI Master          (00001)AMX Corp.           00341 v3.30.371
           (PID=0:OID=0) Serial='210509x2660220',0,0    
           Physical Address=IP 10.0.110.11:1319 (00:60:9f:91:88:d3)
             (00312)vxWorks Image    (00001)                    00381 v3.30.371
             (PID=0:OID=1) Serial=N/A                     
             (00312)BootROM          (00001)                    00340 v3.30.371
             (PID=0:OID=2) Serial=N/A                     
             (00256)AXLink I/F uContr(00001)                    00270 v1.13.7
             (PID=0:OID=3) Serial=0000000000000000
    
  • a_riot42a_riot42 Posts: 1,624
    Maybe I misunderstand the issue. You say both masters are seeing each other and can communicate and ping fine. Then all should be good and I guess I am not seeing the problem.

    If you send an IR Pulse from one master to an IR port on the other you aren't seeing a red IR led flash?

    Are you defining both devices on both systems?
    IE:

    Master 1 system 1
    DEFINE_DEVICE
    dvOtherMaster = 5001:1:2

    Master 2 system 2
    dvOtherMaster = 5001:1:1

    I am not certain that the other masters 5001 address will show up in the online tree of the other if you only have the URL listed and no device in the define_device section of code. I have never encountered this issue so I simply have never looked to see what shows up in the online tree during a M2M install.
    Paul
  • truetrue Posts: 307
    a_riot42 wrote:
    Maybe I misunderstand the issue. You say both masters are seeing each other and can communicate and ping fine. Then all should be good and I guess I am not seeing the problem.

    If you send an IR Pulse from one master to an IR port on the other you aren't seeing a red IR led flash?
    Yes. I do not see a flash. (With an IR file loaded up, of course :))
    Are you defining both devices on both systems?
    IE:

    Master 1 system 1
    DEFINE_DEVICE
    dvOtherMaster = 5001:1:2

    Master 2 system 2
    dvOtherMaster = 5001:1:1
    In code, yes. (Except for System 2, which currently runs no code - no installations at this site do (yet, they're used for port extension), and there are at least 10 that just have an empty program installed). But as I said, I can't even do this from telnet. For example, running this code on System 1 will flash the first serial port transmit LED, but from System 2 the first serial port transmit LED on System 1 will not light up:
    send_string 5001:1:1, 'test'
    I am not certain that the other masters 5001 address will show up in the online tree of the other if you only have the URL listed and no device in the define_device section of code. I have never encountered this issue so I simply have never looked to see what shows up in the online tree during a M2M install.
    Paul
    Of this, I am not certain - I am not running code now to diagnose. I believe it does, but don't have working systems available to me to verify. I'll load up some test code that has these definitions. But I first noticed this issue when I _was_ running code, so...

    I put code on both with those definitions. No change.
  • a_riot42a_riot42 Posts: 1,624
    All I can suggest at that point is to do a dummy check and make sure your dip switches are all ok, etc.

    As for the online tree, I can't really see any good reason why it would show you the 5001 address of the other master. As far as its concerned its just another device like an IR port, correct?
    Paul
  • HedbergHedberg Posts: 671
    I have a working master to master configuration with three masters locate in other parts of the world and one master here. M2M works just fine and when I start up Netlinx studio and "show network", all the devices currently attached to all the masters show up in the tree just as I would expect. But, when I telnet into the master I have here and do the "show system /min" I see exactly what you describe -- no devices on any of the other masters show up, but M2M works just fine. So, I could, of course be wrong, but it appears to me that the results that both you and I are seeing in response to the "show system /min" telnet command do not necessarily indicate a problem.

    It has always been my experience that master to master only works when you have the remote device defined in the code of the master to which you are connected (in the case of telnet). So, if I have masters #1 and #2 and I want to turn on the first IR port on master #2 from master # 1, I must have the IR port on master #2 defined in master #1 code. So, if I do:
    on[5001:9:2,9] in a telnet session on master #1, it will not turn on the IR port on system #2 unless that device (5001:9:2) is defined on system #1 in the define_device section.

    Try populating the define_device sections of the two masters with the devices on the masters that you wish to control via M2M and see what happens.
  • DHawthorneDHawthorne Posts: 4,584
    Only devices defined in the local master will show up in the "show device" or "show system" commands issued to the local master. They will not show you every available device on the remote masters. If you want to actually use a device on a remote master, you still have to define it locally, so this isn't really an issue. I wouldn't call it a bug either, just the way those commands work.
  • HedbergHedberg Posts: 671
    DHawthorne wrote:
    Only devices defined in the local master will show up in the "show device" or "show system" commands issued to the local master. They will not show you every available device on the remote masters. If you want to actually use a device on a remote master, you still have to define it locally, so this isn't really an issue. I wouldn't call it a bug either, just the way those commands work.

    But, in Netlinx Studio, a full list of devices gets displayed using the online tree and display/refresh network whether or not the remote devices are defined locally. Axcent units are a bit different, I think. My recollection is that an Axcent3 is not totally happy unless all devices on the Axlink are properly defined in the program. Doesn't the Axcent Axlink light blink oddly if not all devices are defined? Of course, there is no M2M and remote masters with Axcents as masters.
  • DHawthorneDHawthorne Posts: 4,584
    Hedberg wrote:
    But, in Netlinx Studio, a full list of devices gets displayed using the online tree and display/refresh network whether or not the remote devices are defined locally. Axcent units are a bit different, I think. My recollection is that an Axcent3 is not totally happy unless all devices on the Axlink are properly defined in the program. Doesn't the Axcent Axlink light blink oddly if not all devices are defined? Of course, there is no M2M and remote masters with Axcents as masters.
    Yes, that's how Studio displays, but not the Telnet command. Go figure.
  • truetrue Posts: 307
    Hey all.

    I did populate define_device, and it still wasn't working... swapped gear, and of course everything worked on the new gear. Put the old gear back on - first the NI3100, then the NI900, and it's working now??

    I don't know if it was just me or if I was going crazy or if the gear was going crazy, but it's working as it should now. I'd really like to know what was causing this, though...

    Thanks, all.
  • a_riot42a_riot42 Posts: 1,624
    true wrote:
    Hey all.

    I did populate define_device, and it still wasn't working... swapped gear, and of course everything worked on the new gear. Put the old gear back on - first the NI3100, then the NI900, and it's working now??

    Sure, sure...I believe you. Millions wouldn't, but I do... :)

    Sounds like you maybe had a quirky connection somewhere. Glad to hear you got it working though, I knew it would be something silly, as M2M is pretty straightforward. Sometimes hitting the controller with your fist works for these problems too :)
    Paul