Philips DCN??
J.Y.
Posts: 34
Can somebody help me solve the connection with Philips DCN??
Whatever master is fine.(NI/Axcent3)
thanks.......
Whatever master is fine.(NI/Axcent3)
thanks.......
0
Comments
---
For the Open Interface Software, DIP switches must be set the following:
DIP S14 (PDF page 64, manual page 4-8)
SW 5 off
SW 6 off
SW 7 off
SW 8 on
SW 5 & 6 are defining the user mode (here: SIMPEL protocol)
SW 7 & 8 are the baudrate (here: 19200 Baud)
One more note:
if you are doing a reset at the CCU, the Open Interface Software must be reloaded!
(PDF page 129, Manual 11-1)
---
Page numbers refer to the German manual.
I hope this will help.