Kramer VP729 Presentation Switcher control

Guys need a little help on control of this switcher (not protocol 2000), I can talk to it in hyper terminal (ASCii) all day. But when I try sending the Hex code I get a error back. I know I'm do something wrong here a example of my conversion. ASCii Y 0 0 1 CR I convert to $59,$30,$30,$31,$0D.

Thanks for any suggestions

Brian

Comments

  • sling100sling100 Posts: 123
    You need the 'spaces' ie hex $20 inbetween the actual commands.

    So 'Y 0 0 1 ',CR is not $59,$30,$30,$31,$0D - it is $59,$20,$30,$20,$30,$20,$31,$20,$0D

    Simon
  • sling100sling100 Posts: 123
    Oops too many spaces there... got carried away....

    $59,$20,$30,$20,$30,$20,$31,$0D
  • KouyaKouya Posts: 60
    Simon

    Thanks can't believe this was hanging me up