Home AMX User Forum AMX General Discussion

BACnet - Modbus Master

Hello,
I would like to control a HVAC System that uses the BACnet protocol, through a Modbus Master Bridge of Alerton. I use the Modbus module of AMX but I cannot write anything to the Registers. I can just read the changes made to them. I believe that the problem is that NI and Modbus are both "Master" and I would prefer the Modbus to be Slave. So is there any way to write anything to its registers with this module? Or should I buy another modbus or bacnet bridge??

Any ideas would be really helpful...

Comments

  • You may have a look to the attached Bacnet-IP RS232 solution.

    It's a gateway where an adress table is generated, and so messages are pretty simple on RS232 side, just a packet like "<tableIndex>,<value>" for transferring values from/to Bacnet.

    I can't give any further support to it as it is 3rd party, but I know that it is running well in several installations.
  • PanemPanem Posts: 10
    Marc,

    This was really really helpful!! Thanks a lot for your reply, I appreciate it.

    Best Regards,
    Panos.