Axlink Surge Protection
sonny
Posts: 208
in AMX Hardware
Any recommendations for surge protecting the Axlink port? I have multiple instances of losing thermostats recently, and in this case also lost an RF receiver. Processor made it through this one, thankfully.
Thanks, Sonny
Thanks, Sonny
0
Comments
If you have an Axlink Bus strip very close to the controller, I would use it as my system ground. If not, make a jumper from the Axlink ground connector to system ground.
Also, if your Internet access is from a cable modem, be sure that the incoming cable line is grounded electrically close to the rest of your stuff. I have seen numerous occasions where something came in on the cable line and blew things up that were on the LAN including Axlink devices.
I generally connect the Axlink cable shield to ground at the master controller end only. If the cable loops through an Axlink device, I splice the ground through that device, but do not connect it to the device.
It is my theory that anything picked up by the shield should be drained back to the controller end where the real ground should exist.