Viewstat ENV-VST-C not triggering Compressor
Been getting a bit of a run around with an issue on the ENV-VST-C thermostat. We had this installed for several years without issue then it failed and we sent it in for repair. Since getting it back and using the following set up it won't heat yet I'm certain we haven't changed any wiring or settings. We sent it in for repair again assuming it was a thermostat problem but still have the same issue with a new one.
The set up is:
Single Stage Heat Pump
Electric
Connections are as follows:
RH/RC Power- Red
C Common - Brown
O Reversing valve - white
Y1 Compressor - yellow
G1 Fan - green
When the system calls for cooling the compressor, fan and reversing valve are all energized.
When we call for heat the fan is energized but NOT the compressor and so NO HEAT. (This happens whether or not Axlink is connected.)
We have jumpered W1 to Y1 which is a work around but is not the solution as there seems to be a gap between the fan turning on and the heat kicking in.
The set up is:
Electric
RH/RC Power- Red
C Common - Brown
G1 Fan - green
Sent from my SAMSUNG-SGH-I317 using Tapatalk 2
Gonna check it out but wouldn't that mean that the compressor isn't energized when cooling too? Currently it energizes when cooling but not when heating.
Keep your mode setting as single stage heat pump.
Connect your compressor to W1 and Y1.
Connect your changeover valve to O or B as necessary. The changeover valve is what causes your system to change from a heater to a cooler. Most systems use O to changeover to cool. Some use B to changeover to heat.
The balance point and first stage differential settings would become irrelevant. You will still see the AUX on the screen though when your non-existent backup would have been running.
There is a hotfix firmware available that I would recommend if you plan on using the program mode for setpoint scheduling. It's version 3.12.
What firmware is on the device? You can see it in Studio or on the Axlink channel setting page.