gt-1150 module from AMX
Thomas Hayes
Hi Everyone
I just downloaded the NEC GT-1150 module from AMX and it didn't work. I took a quick look at the reference manual and found the baud rate in the module was written at 9600 and not the projector default of 38400. Not a big issue for me to change the projector baud rate but we have several people in my office that might forget to do this if they had to replace a defective unit. Is there a module by AMX with the default baud(which in my opinion should be the baud used in any module. )
The projector drops voltage level with the higher baudrates, so you may not get the cable lengths you know from other devices. AFAIK this is especially with the NI controllers.
Yes, just not with NEC projectors.
P.S. - be careful if you ever swtich from the GT1150 module to the MT1060 module, or vice-versa. The "RealDev, VirtDev" pair that get passed to the module are reversed on one of 'em.
Yes - I found that one out the hard way.
Unless I?m misunderstanding the question, there shouldn?t be anything to stop you from issuing a SEND_COMMAND SET BAUD to the RS-232 port yourself.
Joe