Home AMX User Forum AMXForums Archive Threads AMX Applications and Solutions
Options

Screen control via IO

Has anyone used the IO ports on a Netlinx product to control screen up/down.
I have a customer that wants to save a few dollars and use the IO ports on an NI700 to control his Draper screen.
It seems possible but I just want to know if anyone has done this.
Thanks
Kenny

Comments

  • Options
    Yes, I have done it, seems to work fine. :)
  • Options
    DHawthorneDHawthorne Posts: 4,584
    You just have to watch the current draw. Other than that, there is no reason not to use them for a hot trigger. The rating for the IO on an NI chassis, for example is 200 mA @ 12 VDC. As long as the Draper trigger doesn't pull more than that (unlikely), you are fine.
  • Options
    KennyKenny Posts: 209
    DHawthorne wrote:
    You just have to watch the current draw. Other than that, there is no reason not to use them for a hot trigger. The rating for the IO on an NI chassis, for example is 200 mA @ 12 VDC. As long as the Draper trigger doesn't pull more than that (unlikely), you are fine.

    I wouldn't think that it would draw that much either but I have never tried controlling a screen with an IO. Relays were always the norm.
    Thanks.
  • Options
    TurnipTruckTurnipTruck Posts: 1,485
    Get yourself a pair of solid state relays, often referred to as SSRs or hockey pucks. They are a high-imedance input and will not attempt to draw enough current that would damage your controller. I beleive the IOs in output mode are open-collector, meaning that you would attach the positive side of both relays to positive voltage on the contoller and the negative side of the relays to the IO outputs.
Sign In or Register to comment.