Diagnostics message unclear....
Line 82 :: ICSPTCPRx31: Ignoring msg from foreign device (same DPS) (IP=0xC0A80134) Cmd=2 DSys=1 DDev=0 TCP Socket=31 IP=192.168.1.52 Index=1 - 11:34:03
Line 83 :: Routing Loop detected. Killing route to system 1. - 11:34:03
Line 84 :: ICSPTCPRx30: Ignoring msg from foreign device (same DPS) (IP=0xC0A80133) Cmd=2 DSys=1 DDev=0 TCP Socket=30 IP=192.168.1.51 Index=0 - 11:34:06
Line 85 :: Routing Loop detected. Killing route to system 1. - 11:34:07
Line 86 :: ICSPTCPRx31: Ignoring msg from foreign device (same DPS) (IP=0xC0A80134) Cmd=2 DSys=1 DDev=0 TCP Socket=31 IP=192.168.1.52 Index=1 - 11:34:07
Line 87 :: Routing Loop detected. Killing route to system 1. - 11:34:07
the above is copied out of my diagnostics window. these messages seem to appear now and again, and im unsure why they do. they don't seem to adversely affect the system, but i'd like to know if there is a problem....
the AMX system is an NI-3100 as master and running all code (diagnostics was taken from this processor), with two NI-900's connected via IP which contain no code, and are just used as extra control ports.
NI-3100: IP = 192.168.1.50, Device 1, System 1
NI-900 1: IP = 192.168.1.51, Device 1, System 2
NI-900 2: IP = 192.168.1.52, Device 1, System 3
The URL listing table is only present in the NI-3100 and only contains the IP addresses of the two NI-900s.
Can anyone shed any light?
mark
mark
Do you have rebooted the masters after setting the system numbers?
You can check that for example by terminal/telnet with the SHOW DEVICE command:
>show device Local devices for system #2 (This System) ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00285)NI Master (00001)AMX Corp. 00296 v3.21.343 (PID=0:OID=0) Serial=0,0,0,0,0,0,0,0,0,0,0,0, Physical Address=IP 172.16.100.12:1319 (00:60:9f:90:bc:39) (00285)vxWorks Image (00001) 00296 v3.21.343 (PID=0:OID=1) Serial=N/A (00285)BootROM (00001) 00298 v3.00.316 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 05001 (00286)NI-3000 (00001)AMX Corp. 00299 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection 33001 (65534)Virtual (00001)AMX Corp. 00296 v3.21.343 (PID=0:OID=0) Serial=0,0,0,0,0,0,0,0,0,0,0,0, Physical Address=NoneSo my system here has system number #2.
I am sure all the processors are set to different system numbers. The system numbers were set when i first installed the equipment, and all processors have been rebooted many times during the programming of the system! The code running in the master NI-3100 references the two NI-900 ports with their respective system numbers (2 and 3) and works fine.
when i next get back on site i will double check this via telnet, but I'm pretty sure the system numbers are correct.
> show system Local devices for system #1 (This System) ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00299)NI Master (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=IP 10.1.1.200:1319 (00:60:9f:91:d4:11) (00299)vxWorks Image (00001) 00378 v3.21.343/0 (PID=0:OID=1) Serial=N/A (00299)BootROM (00001) 00379 v3.21.343 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 00128 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00129 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00130 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00131 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00132 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00133 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00134 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00135 (00188)COLOR LCD TOUCH PAN(00001)AMX Corp. 32786 v5.12b (PID=0:OID=0) Serial=0000000000000000 Physical Address=Axlink 00150 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00151 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00152 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00153 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00154 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00156 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 00157 (00224)Mio Modero (00001)AMX Corp. 00000 v-.-- (PID=0:OID=0) Serial=Unknown Physical Address=Axlink 05001 (00286)NI-3100 (00001)AMX Corp. 00383 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection 10001 (00288)MVP 7500 (00001)AMX Corp. 00400 v2.72.2 (PID=0:OID=0) Serial='596501X4760187',0,0 Physical Address=IP 10.1.1.209 (00288)Kernel (00001) 00401 2.4.20-2 (PID=0:OID=2) Serial=N/A (00288)Root File System (00001) 00402 v2.72.2 (PID=0:OID=3) Serial=N/A (00288)Bootrom (00001) 00403 v2.72.2 (PID=0:OID=4) Serial=N/A (00288)Sensor (00001) 00404 v2.72 (PID=0:OID=5) Serial=N/A (00288)Opt File System (00001) 00405 v2.72.2 (PID=0:OID=6) Serial=N/A (00288)Battery Base (00001) 00308 2.04 (PID=0:OID=7) Serial=N/A 10002 (00288)MVP 7500 (00001)AMX Corp. 00400 v2.72.2 (PID=0:OID=0) Serial='596501X0670339',0,0 Physical Address=IP 10.1.1.210 (00288)Kernel (00001) 00401 2.4.20-2 (PID=0:OID=2) Serial=N/A (00288)Root File System (00001) 00402 v2.72.2 (PID=0:OID=3) Serial=N/A (00288)Bootrom (00001) 00403 v2.72.2 (PID=0:OID=4) Serial=N/A (00288)Sensor (00001) 00404 v2.72 (PID=0:OID=5) Serial=N/A (00288)Opt File System (00001) 00405 v2.72.2 (PID=0:OID=6) Serial=N/A 10005 (00304)DMS (00001)AMX Corp. 00353 v1.00.120 (PID=0:OID=0) Serial=240801WHX4660139 Physical Address=IP 10.1.1.208 32001 (00262)NSX Application (00001)AMX Corp. 00281 2.50 (PID=0:OID=0) Serial=0,0,0,0,0,0,0,0,0,0,0,0, Physical Address=IP 10.1.1.103 33002 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 33003 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 33004 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 33005 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 33006 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 33015 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 34000 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None 34001 (65534)Virtual (00001)AMX Corp. 00380 v3.21.343 (PID=0:OID=0) Serial='210515x4860218',0,0 Physical Address=None Local devices for system #2 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00298)NI Master (00001)AMX Corp. 00341 v3.21.343 (PID=0:OID=0) Serial='210503x4760160',0,0 Physical Address=IP 10.1.1.201:1319 (00:60:9f:91:d1:cc) (00298)vxWorks Image (00001) 00339 v3.21.343 (PID=0:OID=1) Serial=N/A (00298)BootROM (00001) 00340 v3.21.343 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 05002 (00286)NI-700 (00001)AMX Corp. 00346 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection Local devices for system #3 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00298)NI Master (00001)AMX Corp. 00341 v3.12.335 (PID=0:OID=0) Serial='210503x3460928',0,0 Physical Address=IP 10.1.1.202:1319 (00:60:9f:91:a5:70) (00298)vxWorks Image (00001) 00257 v3.12.335 (PID=0:OID=1) Serial=N/A (00298)BootROM (00001) 00340 v3.00.316 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 05003 (00286)NI-700 (00001)AMX Corp. 00346 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection Local devices for system #4 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00298)NI Master (00001)AMX Corp. 00341 v3.12.335 (PID=0:OID=0) Serial='210503x3460740',0,0 Physical Address=IP 10.1.1.203:1319 (00:60:9f:91:a6:0f) (00298)vxWorks Image (00001) 00257 v3.12.335 (PID=0:OID=1) Serial=N/A (00298)BootROM (00001) 00340 v3.00.316 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 05004 (00286)NI-700 (00001)AMX Corp. 00346 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection Local devices for system #5 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00298)NI Master (00001)AMX Corp. 00341 v3.21.343 (PID=0:OID=0) Serial='210503x4760148',0,0 Physical Address=IP 10.1.1.204:1319 (00:60:9f:91:d1:87) (00298)vxWorks Image (00001) 00339 v3.21.343 (PID=0:OID=1) Serial=N/A (00298)BootROM (00001) 00340 v3.21.343 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.12.140 (PID=0:OID=3) Serial=0000000000000000 05005 (00286)NI-700 (00001)AMX Corp. 00346 v1.12.140 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection Local devices for system #6 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00312)NI Master (00001)AMX Corp. 00341 v3.21.343 (PID=0:OID=0) Serial='210509x0460277',0,0 Physical Address=IP 10.1.1.205:1319 (00:60:9f:91:5d:d6) (00312)vxWorks Image (00001) 00381 v3.21.343 (PID=0:OID=1) Serial=N/A (00312)BootROM (00001) 00340 v3.21.343 (PID=0:OID=2) Serial=N/A 05006 (00286)NI-900 (00001)AMX Corp. 00382 v1.10.127 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal Connection Local devices for system #7 ---------------------------------------------------------------------------- Device (ID)Model (ID)Mfg FWID Version 00000 (00312)NI Master (00001)AMX Corp. 00341 v3.21.343 (PID=0:OID=0) Serial='210509x1260094',0,0 Physical Address=IP 10.1.1.206:1319 (00:60:9f:91:6e:47) (00312)vxWorks Image (00001) 00381 v3.21.343 (PID=0:OID=1) Serial=N/A (00312)BootROM (00001) 00340 v3.21.343 (PID=0:OID=2) Serial=N/A (00256)AXLink I/F uContr(00001) 00270 v2.01.126 (PID=0:OID=3) Serial=0000000000000000 05007 (00286)NI-900 (00001)AMX Corp. 00382 v1.10.127 (PID=0:OID=0) Serial='N/A',0,0,0,0,0,0,0,0,0, Physical Address=Internal ConnectionI have the WHC control master which is system 1 pointing to the others:
Here is my url list
getting this error message
Any ideas???
You may have a URL setup from the main master (system 1) to the 2 secondary masters (systems 2,3) and then systems 2,3 back to the main master.
You only need to do an URL from the 2 secondary masters to the main one. That sets up the two-way communication from all three masters.
To state it another way, you do not need to enter in any URL link from the main system master (system 1)
This error is most likely NOT becuase of your master to master setup. I once had this problem aswell. What's causing the error is you have an event (most likely a level event) that gets sent to one master. Triggers and event there. Then info gets sent back to the original master, triggers and event there. The orignal master then triggers an event back to the remote master... etc... Bascially, an Infinite loop starts. Level Events are usually the main cause of this. Comment Out some level events on one of your masters until you find the event causing the inifinite loop. Then figure out how to prevent it.