trigger timed gain via crestron via tcp connection

I am able to trigger a timed gain via logic but want to do it via a crestron control system i ma having trouble finding the coed for each of the 4 trigers

Comments

  • Options
    You simply need to determine the correct command string for those Logic Source buttons. In London Architect, you will see the DI Toolbar at the top of the screen. This shows the string of any control that you operate. You can operate a control in Design Mode by holding down the ALT key.
    The DI Toolbar, by default, displays the string in decimal format. You need to change it to Hex format. You can change the DI Toolbar settings by clicking on the elipsis on the right hand side.
    Once setup to Hex format, simply ALT-click you Logic Sources. Note that there is one command for ON and one for OFF. You will see the command strings appear in the DI Toolbar. You can use these commands over RS-232 or Ethernet TCP port 1023.
    RS-232 settings of the Soundweb are in the Properties. By default it is set to 115200 Baud.