AXLINK OVER CAT 5
Clingpeach
Posts: 156
Is this doable. Or not a good idea? Its for the new AMX Thermostats?
0
Comments
No problem on the data across one of the pairs - issue is power.
The other issue is the voltage drop over the cable. You really cannot go very far. The official legth is something like 30 feet. I've inherited a system that was done in all CAT5. I'd love to slap the person who did it. They used some of the same run for IR, RS232 and AxLink. There is one run that has all this and power too. They all share a ground wire.
My advice is avoid using it if possible.
What does it matter?
a) you use Cat 5
b) you use certified AXLink cable
?
Well, Lutron uses that wire incidetally. It's the exact same wire.
Actually, Axlink is a great communication method. To be frank, I wish they'd use it for more things.
As for CAT5 and CAT6 and why or why not use if for other things...
It has a lot to do with the physics. single core wire is best used for AC and multi-stranded wire is best for DC. Technically standard networking is DC. But due to the fact that it operates in the MHZ or GHZ range, it tends to act a lot like AC.
I can tell you that elecrical engineers have migrains over how folks like us misuse wire. When we use the wrong wire for a job, there's no way to guaranty the performance. It's stuff like this that creates some of the flakiness of gear operation.
I've been in houses where I've seen speaker level over a couple strads of CAT5e. It was meant for network and telephone.
But, whatever gets the gig done I suppose...
CAT 5 is not the right cable to use, but if you have to, no worries.
http://www.amx.com/techsupport/techNote.asp?id=146
This isn't an issude for short runs but it coulf really cause major issues on long runs.
Your digital 1's and 0's should be very square but with the wrong capacitance it could turn into more of an AC wave.
Professionally speaking I would use the proper cable.
This is exactly why Cat5 makes a good Axlink cable. Cat5 is a low-capacitance cable.
Axlinx (or any other digital data circuit) is not looking for a specific cpacitance. The goal is to minimize the capacitance by using the lowest capacitance interconnects possible.
The effect of capacitance on data is cumulative with total cable length in the circuit. Therefore, with ten 100-foot home-runs to an Axlink bus strip, the total capacitance would be that of 1000 feet of wire.
With 15pF per foot cable, I beleive the Axlink maximum length spec is 3500 feet. Therefore with wire of twice the capacitance, you would cut the maximum allowable length in half.
If you can run wire, I would, in this case. I generally use Lutron keypad wire for such jobs, since I always have tons of it on hand. I'm also to the point where I will run two Cat 5's and either a 4/18 shielded cable or 7/18 to any control location, whether I think I will need it or not.
http://www.amx.com/techsupport/techNote.asp?id=464
Liberty Wire and Cable, www.libertycable.com, and Comprehensive Video, www.comprehensivevideo.com,both sell cables specifically designed for use with a network like AXlink. Here are some features of these special-purpose cables:
one 22 AWG pair of separately-shielded, low-capacitance (12.5pF/ft) conductors for data. Low capacitance allows the data to travel further without degradation. Shielding reduces induction of noise from other sources, as well as emission of noise into susceptible nearby circuits.
one 18 AWG pair of conductors for power. Relatively high capacitance (35-50 pF/ft) serves to filter noise from the power source. The larger wire means reduced resistance, which allows for greater distances.
As previously stated the real problem is power which you would also have with ICSNET.
So run shielded CAT5/6 cable and you have future proofed your install.
Read this if you want in depth info.
http://www.maxim-ic.com/appnotes.cfm/an_pk/763
<number of conductors>/<wire gauge>, so that's 4-conductor, 18 gauge and 7-conductor, 18 gauge, respectively.
A tech note was just released on this subject.
http://www.amx.com/techsupport/techNote.asp?id=907
The referenced PDF linked to the tech note pretty much spells out best practices for using CATx for Axlink cable runs.